International sales & support DesignBuilder USA website DesignBuilder China website DesignBuilder Australia website DesignBuilder France website DesignBuilder Mexico website DesignBuilder Portugal website DesignBuilder Italy website DesignBuilder South Africa website DesignBuilder Brazil website DesignBuilder Japan website DesignBuilder Spain website DesignBuilder India website DesignBuilder Chile website
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Air permeability for existing buildings

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EPCs and Part L
View previous topic :: View next topic  
Author Message
cdbhaumik



Posts: 8
PostPosted: Mon Oct 27, 2008 3:45 pm    Post subject: Air permeability for existing buildings Reply with quote

When producing an EPC for an existing building where a pressure test hasn't been carried out, is it acceptable to use the default air permeability of 10 m^3/hour/m^2? Or are there published figures somewhere for older buildings? I was thinking that 10 might be a bit optimistic for some older buildings!

Thanks, Claire
Back to top
View user's profile Send private message
Pilch



Posts: 71
PostPosted: Mon Oct 27, 2008 5:24 pm    Post subject: Reply with quote

Hello Claire
I was told on my level 4 training to use 25 for buildings constructed before 2002, 10 for buildings constructed between 2002 and 2006 and 15 for anything since 2006.
Back to top
View user's profile Send private message
cdbhaumik



Posts: 8
PostPosted: Thu Nov 27, 2008 9:58 am    Post subject: Reply with quote

This isn't mentioned in any of the documentation. It could be a better idea to use the default of 10 (although it is optimistic) at least it will be consistent.
Back to top
View user's profile Send private message
PaulCarey



Posts: 20
Location: Stalybridge, Nr Manchester
PostPosted: Thu Nov 27, 2008 11:56 pm    Post subject: RE: Air permeability for existing buildings Reply with quote

Claire

My comments below:

When producing an EPC for an existing building where a pressure test hasn't been carried out, is it acceptable to use the default air permeability of 10 m^3/hour/m^2?

No not really, I thought you were meant to assume a value of 15m3/hr.m2 much like you would in Part L calculations if it isn't tested.

Or are there published figures somewhere for older buildings?

There are some available from the AIVC but I imagine these are getting a bit dated now. They might be a useful source for older buildings though.


I was thinking that 10 might be a bit optimistic for some older buildings!

For some maybe, but then there are some pretty bad new ones about too.


Thanks, Claire
Back to top
View user's profile Send private message Visit poster's website
Andrew Bairstow
Site Admin


Posts: 315
Location: Birmingham, UK
PostPosted: Sat Nov 29, 2008 11:18 am    Post subject: Reply with quote

The value of 25 for existing buildings has come directly from CLG. I am unaware of it being documented, we simply have had an email from the EPBD dept at CLG advising us of this change. For buildings post 2002 then you should use the guidelines in the 2002 Part L2 (attached). I use the following guidelines which I have deduced from the 2002 and 2006 regs:

2002-2006 and < 500m2. The problem occurs when the building owner cannot supply a test result when the building should have been tested. Whilst new buildings over 500m2 should have a test certificate showing less than 10 some flexibility was put in place for buildings not achieving an initial result <= 10m3/m2/hour based on an improvement factor.
All very confusing!
Andrew Confused



PartL2_2002.pdf
 Description:

Download
 Filename:  PartL2_2002.pdf
 Filesize:  375.5 KB
 Downloaded:  983 Time(s)


_________________
Andrew Bairstow
DesignBuilder Software
Back to top
View user's profile Send private message Visit poster's website
Andrew Bairstow
Site Admin


Posts: 315
Location: Birmingham, UK
PostPosted: Mon Dec 01, 2008 11:21 am    Post subject: Reply with quote

Sorry all about last post seems my insert did not work so here goes again:
The value of 25 for existing buildings has come directly from CLG. I am unaware of it being documented, we simply have had an email from the EPBD dept at CLG advising us of this change. For buildings post 2002 then you should use the guidelines in the 2002 Part L2 (attached). I use the following guidelines which I have deduced from the 2002 and 2006 regs:

pre 2002: 25m3/m2/hour
2002-2006 1000m2: 11.5m3/m2/hour (or test result)
2006+: 15m3/m2/hour (or test result)

The problem occurs when the building owner cannot supply a test result when the building should have been tested (2002-2006 mandatory over 1000m2, 2006+ mandatory over 500m2). Whilst recent medium sized buildings should have a test certificate showing less than 10 some flexibility was put in place for buildings not achieving an initial result <= 10m3/m2/hour based on an improvement factor.
Andrew

_________________
Andrew Bairstow
DesignBuilder Software
Back to top
View user's profile Send private message Visit poster's website
johnmcc



Posts: 11
PostPosted: Mon Feb 16, 2009 12:18 pm    Post subject: Confusing Reply with quote

This is a confusing topic as, sometimes DB defaults to 10 and sometimes its defualt to 25, not sure where it takes its information to make this assumption. Working on an offices building 1970s construction and its defaulting to 10, but other industrial units 1930s contruction have been defaulting to 25. Would be nice to see some clear direction from the CLG?
Back to top
View user's profile Send private message
Andrew Bairstow
Site Admin


Posts: 315
Location: Birmingham, UK
PostPosted: Thu Feb 19, 2009 2:49 pm    Post subject: Reply with quote

It should be when you first specify the type of assessment (add building) that the air permeability is set. If you set Build Regs then it should be set as 10, if EPC it should be 25. If there are circumstances where this changes depending on building type then please let us know. I am not aware that this parameter is set when selecting building type or construction type. Would you like to check this again and let us know if it is still happening.
Andrew

_________________
Andrew Bairstow
DesignBuilder Software
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EPCs and Part L All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B