International sales & support DesignBuilder USA website DesignBuilder China website DesignBuilder Australia website DesignBuilder France website DesignBuilder Mexico website DesignBuilder Portugal website DesignBuilder Italy website DesignBuilder South Africa website DesignBuilder Brazil website DesignBuilder Japan website DesignBuilder Spain website DesignBuilder India website DesignBuilder Chile website
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

CFD siumlation and ceilling

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD
View previous topic :: View next topic  
Author Message
thanhtruc



Posts: 11
PostPosted: Fri May 13, 2011 3:19 am    Post subject: CFD siumlation and ceilling Reply with quote

Hi,
I am modelling air distribution for a seven floor building. The result is quite "strange" when the air flow can pass through the slab of closed-ceiling, no hole for air in. I have tried to set the grid spacing is the same with the height of the floor. Could you suggest me how to solve this problem to make the CFD result more realistic?
Thanks for any suggestion, shared experiment.
Best regards,
Truc Pham
Back to top
View user's profile Send private message
Steve Potter



Posts: 572
Location: newcastle
PostPosted: Sat May 14, 2011 5:04 pm    Post subject: Reply with quote

Hi Truc,

Could you upload your model to the forum so that we can take a look at it? Perhaps you could also indicate which ceiling is exhibiting this problem.

Regards,

Steve
Back to top
View user's profile Send private message
thanhtruc



Posts: 11
PostPosted: Mon May 16, 2011 1:35 am    Post subject: CFD and ceiling's slab Reply with quote

Hi Steve,
Please find the attached model. the ceiling of the 4th floor and above have the CFD result problem that the air get through the slab.
Thanks and look forward to your feedback.
Regards,
Truc Pham



110513_GC_Atrium.rar
 Description:

Download
 Filename:  110513_GC_Atrium.rar
 Filesize:  3.12 MB
 Downloaded:  292 Time(s)

Back to top
View user's profile Send private message
Steve Potter



Posts: 572
Location: newcastle
PostPosted: Mon May 16, 2011 8:46 am    Post subject: Reply with quote

Truc,

You have specified such a large grid line merge tolerance (0.5m) that the grid lines that would normally coincide with the faces of the slabs are being merged together and consequently the floor slabs are being 'dropped out' altogether.

Generally speaking, it is a good idea to use as low a grid line merge tolerance as possible to achieve acceptable cell aspect ratios without losing too much in the way of model detail. With your model, if you use a default grid spacing of 0.5m and a grid line merge tolerance of 0.05m, you should find that these settings result in a relatively low aspect ratio and the floor slabs will be retained.

Hope this is of help.

Regards,

Steve
Back to top
View user's profile Send private message
thanhtruc



Posts: 11
PostPosted: Mon May 16, 2011 9:55 am    Post subject: CFD and ceiling's slab Reply with quote

Hi Steve,
Thank you very much for your suggestion. it worked out Smile.
Regards,
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B