International sales & support DesignBuilder USA website DesignBuilder China website DesignBuilder Australia website DesignBuilder France website DesignBuilder Mexico website DesignBuilder Portugal website DesignBuilder Italy website DesignBuilder South Africa website DesignBuilder Brazil website DesignBuilder Japan website DesignBuilder Spain website DesignBuilder India website DesignBuilder Chile website
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Default lighting values in Data Reflection Report?

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EPCs and Part L
View previous topic :: View next topic  
Author Message
BennieM



Posts: 3
PostPosted: Wed Aug 17, 2011 3:06 pm    Post subject: Default lighting values in Data Reflection Report? Reply with quote

Hi there,

Can anyone think of a reason why despite using either design or chosen lighting values, it makes no difference to the results displayed in the Data Reflection Report?

I have a laboratory which is effectively 1 zone, and i have entered the lighting as "Designed" giving a W/m2 of 12 and a Lux value of 520. The area of the building is 200m2 so it should show the total wattage as 2400W, however in the report it shows this as 3700W and the Lux value is 800.

I can get this value to change in the Data reflection report by changing the activity of the zone, but again it seems to be giving me default values instead of the actual values I have entered.

Any help on the matter would be greatly appreciated.

Thanks
Craig
Back to top
View user's profile Send private message
Andrew Bairstow
Site Admin


Posts: 343
Location: Birmingham, UK
PostPosted: Wed Aug 17, 2011 4:16 pm    Post subject: Reply with quote

Craig
SBEM derives the equivalent circuit power assuming that the installed lighting provides the NCM standard illuminance for the activity and then rounds this to the nearest 50W (for BRUKL output). In your example the circuit power would thus be:
12 x 200 * 800 / 520 = 3692 (3700 to nearest 50W)

Regards
Andrew

_________________
Andrew Bairstow
DesignBuilder Software
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EPCs and Part L All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B