Topic: Error RhoAir is calculated as less than 0 |
jteasterling
Replies: 1
Views: 1882
|
Forum: EnergyPlus General Posted: Thu Feb 28, 2013 9:46 pm Subject: Error RhoAir is calculated as less than 0 |
SOLUTION:
The air temperature distribution seems to be the culprit.
I had it on "Dynamic Gradient". Changing it to "Mixed" seems to solve the problem.
I've had issues with dynamic gradient be ... |
Topic: Error RhoAir is calculated as less than 0 |
jteasterling
Replies: 1
Views: 1882
|
Forum: EnergyPlus General Posted: Thu Feb 28, 2013 7:04 pm Subject: Error RhoAir is calculated as less than 0 |
The following error is terminating my simulation:
** Severe ** PsyRhoAirFnPbTdbW: RhoAir (Density of Air) is calculated <= 0 [-0.54872].
** ~~~ ** pb =[78482.60], tdb=[-771.03], w=[5.95 ... |
Topic: Templates Affecting Fields Across Tabs |
jteasterling
Replies: 1
Views: 1089
|
Forum: EnergyPlus General Posted: Tue Feb 05, 2013 10:43 pm Subject: Templates Affecting Fields Across Tabs |
| I was recently doing some trouble shooting and it took me a while to realize that templates for certain tabs would affect fields on other tabs. My biggest issue was that the Activity Template was affe ... |
Topic: 7/12 Schedules Seem to be Nonfunctional |
jteasterling
Replies: 1
Views: 1433
|
Forum: EnergyPlus General Posted: Tue Feb 05, 2013 10:34 pm Subject: 7/12 Schedules Seem to be Nonfunctional |
I am having trouble using the 7/12 schedules. I am not new to DB or E+. Templates that I have been using for the past 5 years are no longer functioning.
I've narrowed it down to the use of 7/12 sch ... |
Topic: Simulation Wont Heat |
jteasterling
Replies: 2
Views: 1134
|
Forum: EnergyPlus General Posted: Tue Feb 05, 2013 10:27 pm Subject: Simulation Wont Heat |
7/12 schedules seem to be broken.
I'm starting a new thread to discuss. |
Topic: Simulation Wont Heat |
jteasterling
Replies: 2
Views: 1134
|
Forum: EnergyPlus General Posted: Tue Jan 29, 2013 11:49 pm Subject: Simulation Wont Heat |
It seems that the problem is the Activity Template that I've been using for the past 5 years. I haven't figured out exactly what's wrong with it, but it is not functioning properly.
I don't believe ... |
Topic: Simulation Wont Heat |
jteasterling
Replies: 2
Views: 1134
|
Forum: EnergyPlus General Posted: Tue Jan 29, 2013 2:06 am Subject: Simulation Wont Heat |
The heating and cooling design sims seem to be working fine.
The full simulation, however, will not heat to set points.
I've attached the model.
Any thoughts?
Thanks. |
Topic: Need ventilation setpoint schedules & Clothing setback |
jteasterling
Replies: 5
Views: 1914
|
Forum: EnergyPlus General Posted: Fri May 25, 2012 7:41 pm Subject: Need ventilation setpoint schedules & Clothing setback |
I'm having issues with this as well.
I would like CLO scheduling for summer night time ventilation comfort analysis.
Thanks,
John |
Topic: Strange Cooling Load to Heat Gain Discrepancy |
jteasterling
Replies: 6
Views: 2492
|
Forum: EnergyPlus General Posted: Mon May 14, 2012 3:51 pm Subject: Strange Cooling Load to Heat Gain Discrepancy |
Interesting.
I didn't realize that I had a schedule effecting me.
The lack of weird spiking looks good but it still seems like a major increase in cooling load.
If you allow a room to strati ... |
Topic: Heat Balance very Unbalanced |
jteasterling
Replies: 4
Views: 3367
|
Forum: EnergyPlus General Posted: Fri May 11, 2012 4:32 pm Subject: Heat Balance very Unbalanced |
I'm still seeing crazy partition gains in the cooling design tab when surface variables are on.
It doesn't seem to be effecting anything as far as AC use or sizing, but it makes the graphs hard to ... |
Topic: Strange Cooling Load to Heat Gain Discrepancy |
jteasterling
Replies: 6
Views: 2492
|
Forum: EnergyPlus General Posted: Thu May 10, 2012 8:41 pm Subject: Strange Cooling Load to Heat Gain Discrepancy |
I've found the source of the issue and an easy way to reproduce what I'm seeing:
-Draw a 20'x20' box and allow it to autocomplete with default values.
-Set location (weather, etc) to Salt Lake Cit ... |
Topic: Parametric Simulation Units Issue |
jteasterling
Replies: 0
Views: 2374
|
Forum: EnergyPlus General Posted: Mon May 07, 2012 5:45 pm Subject: Parametric Simulation Units Issue |
Hi Guys,
Using the parametric simulation as follows:
Criteria/Data = 3-Operative Temp
Variable = % External Window Operable (set from 0%-100%)
The simulation seems to be working fine however ... |
Topic: Strange Cooling Load to Heat Gain Discrepancy |
jteasterling
Replies: 6
Views: 2492
|
Forum: EnergyPlus General Posted: Mon Apr 30, 2012 5:02 pm Subject: Strange Cooling Load to Heat Gain Discrepancy |
| I've modeled a small house and I am seeing a strange discrepancy between cooling load and heat gain. When I export all of the gains and losses and sum them, then compare them to the cooling load the t ... |
Topic: Wall Thickness and Local Shading |
jteasterling
Replies: 3
Views: 2064
|
Forum: EnergyPlus General Posted: Wed Apr 11, 2012 3:19 pm Subject: Wall Thickness and Local Shading |
| So does the outer surface only "exist" for visualization purposes? ie all heat transfer is though the inner surface, window is on inner surface, outer surface does not shade windows on inner surface, ... |
Topic: Wall Thickness and Local Shading |
jteasterling
Replies: 3
Views: 2064
|
Forum: EnergyPlus General Posted: Tue Apr 10, 2012 8:29 pm Subject: Wall Thickness and Local Shading |
I am confused about how the local shading is working.
I am modeling a house that has walls that are 1' thick and overhangs on the south side that project 1.5' out from the outer wall. When I enter ... |
| |