Posted: Tue Oct 18, 2011 10:27 pm Post subject: Removing a heating coil from fan coil unit |
|
|
Hi all,
Just wondering if there is a way in the detailed HVAC to have a fan coil unit with only a cooling coil? It doesn't appear that I am able to remove the heating coil from the unit when I add it to my zone?
I know I can turn it off in my availability schedule but I will still need to connect the heating coil to the HW loop to avoid errors.
It would be great if I was able to remove the heating coil completely.
Is there a way?
Thanks for your time on this.
Celia |
|
| Back to top |
|
 |
Andy Tindale

Posts: 2619 Location: Stroud |
Posted: Thu Oct 20, 2011 2:30 pm Post subject: |
|
|
Hi Celia,
FCU must have a heating coil so there is no way to do this in DB. As you say, simply add a hot water loop and set the availability schedule for heating to be off.
Andy |
|
| Back to top |
|
 |
celiaks
Posts: 18
|
Posted: Fri Oct 21, 2011 9:28 pm Post subject: |
|
|
| Thanks Andy! |
|
| Back to top |
|
 |
jamo0312see
Posts: 83
|
Posted: Fri Mar 23, 2012 2:16 am Post subject: setting heating coils to use electric in FCU = errors |
|
|
** Severe ** GetFanCoilUnits: ZoneHVAC:FourPipeFanCoil="GROUNDFLOOR:EOL%TST100KE.PRMTR FAN COIL UNIT", invalid
** ~~~ ** illegal value: Heating Coil Object Type="COIL:HEATING:ELECTRIC".
above is an example of error |
|
| Back to top |
|
 |
Andy Tindale

Posts: 2619 Location: Stroud |
Posted: Fri Mar 23, 2012 8:46 am Post subject: |
|
|
Are you using a recent version of DB? I mean v3.0.0.104 or later? If not could you try upgrading? If this doesn't help then please send your dsb file to the DesignBuilder support desk for us to check.
Andy |
|
| Back to top |
|
 |
jamo0312see
Posts: 83
|
Posted: Sat Mar 24, 2012 3:03 am Post subject: |
|
|
my DB version is v3.0.0.105 when my errors occur..
and yes these is the same project has in the other thread..
"Adding FCUs to zone group generate errors pls help"
also my zone group has 3 components, consisting of an ADU(direct air), Extract air and FCU(note: heating is electric and coiling is water with chillers and cooling tower), which is supplied via AHU (also with cooling via CW & CT, but no heating). simulating with errors. |
|
| Back to top |
|
 |
fabiano.ferreira
Posts: 3
|
Posted: Mon Apr 16, 2012 12:10 pm Post subject: |
|
|
Hi,
I'm trying to model a fancoil system only a cooling coil. As we cannot exclude the heating coil from the fancoil unit and instead of modeling the heating coil and set it to not operate, Can I model the system as an airloop system?
Regards,
Fabiano |
|
| Back to top |
|
 |
Andy Tindale

Posts: 2619 Location: Stroud |
Posted: Thu Apr 19, 2012 4:43 am Post subject: |
|
|
Hi Fabiano,
FCU are zone systems and cannot serve multiple zones but you could probably set up a generic air loop with AHU system that provided similar conditioning.
Andy |
|
| Back to top |
|
 |
fabiano.ferreira
Posts: 3
|
Posted: Thu Apr 19, 2012 12:18 pm Post subject: |
|
|
ok! Thanks Andy.
So every time that I've a got a FCU serving more than one zone I have to model the system with an Airloop system?
Fabiano |
|
| Back to top |
|
 |
Andy Tindale

Posts: 2619 Location: Stroud |
Posted: Thu Apr 19, 2012 3:38 pm Post subject: |
|
|
| Yes that's right. |
|