International sales DesignBuilder USA DesignBuilder China DesignBuilder Australia DesignBuilder France DesignBuilder Mexico DesignBuilder Portugal DesignBuilder Italy DesignBuilder South Africa DesignBuilder Brazil DesignBuilder Japan DesignBuilder Spain DesignBuilder India DesignBuilder Chile DesignBuilder Czech Replublic, Poland, Hungary, Slovakia DesignBuilder Israel DesignBuilder Greece DesignBuilder South East Asia DesignBuilder Iran DesignBuilder Germany
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

VAV Terminal Box with VSD fan

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus General
View previous topic :: View next topic  
Author Message
celiaks



Posts: 18
PostPosted: Thu Oct 27, 2011 11:52 pm    Post subject: VAV Terminal Box with VSD fan Reply with quote

Hi!

I am getting the following error when I try to model a VAV terminal box with a VSD fan.

During AirTerminal:SingleDuct:VAV:Reheat:VariableSpeedFan Input, Invalid Component Name input=ANDARTIPO04:ESCRITORIOINTERNO SINGLE DUCT VAV REHEAT VS FAN 1 SUPPLY FAN
** ~~~ ** Component type=FAN:VARIABLEVOLUME
** ~~~ ** In AirTerminal:SingleDuct:VAV:Reheat:VariableSpeedFan = ANDARTIPO04:ESCRITORIOINTERNO SINGLE DUCT VAV REHEAT VS FAN 1

So it seems to have a problem with the connection between the VAV supply fan in the AHU and the VSD fan in the terminal. Am I interpreting correctly?
If I go to change the AHU fan to Constant Volume it won't make this input available.
Does anyone have any suggestions on how to fix this problem?

Thank you in advance.

Celia
Back to top
View user's profile Send private message
Andy Tindale



Posts: 2617
Location: Stroud
PostPosted: Fri Oct 28, 2011 1:09 am    Post subject: Reply with quote

Celia,

Have you tried reducing the length of the block and zone names to see if that helps? I just wonder if you are running into E+ name size limits of some sort?

If not could you send the dsb file?

Andy
Back to top
View user's profile Send private message Visit poster's website
celiaks



Posts: 18
PostPosted: Fri Oct 28, 2011 3:02 pm    Post subject: Reply with quote

I will try and reduce the names for the blocks and zones. I have attached the file for your review!

Thanks!
Celia



Bay View_System7.dsb
 Description:

Download
 Filename:  Bay View_System7.dsb
 Filesize:  2.21 MB
 Downloaded:  56 Time(s)

Back to top
View user's profile Send private message
Andy Tindale



Posts: 2617
Location: Stroud
PostPosted: Mon Oct 31, 2011 4:29 pm    Post subject: Reply with quote

Celia,

We've had a good look at your model and found a couple of things:

a) There is a problem with DB where the Plant equipment operation "Scheme Operation Type" is not set. This is caused by a versioning problem where DB has failed to translate correctly from an old format to the new format. You can solve this by manually changing the Scheme Operation Type in the chilled water and condensor loop dialogs back the original settings.

b) If you make the fix desribed in a) and re-simulate you will come across a whole new lot of errors which seem to be related to using an electric heating coil in the variable speed fan ADUs instead of a water coil. We have requested help from E+ support on this and will let you know when we hear back.

Andy
Back to top
View user's profile Send private message Visit poster's website
Andy Tindale



Posts: 2617
Location: Stroud
PostPosted: Tue Nov 01, 2011 12:56 pm    Post subject: Reply with quote

It turns out to be an E+ problem with using electric heating coils in the variable speed fan ADUs and their developers are aiming to get a fix into E+ v7 which is due for release very soon.

In the meantime can you use water heating coils?

Andy
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus General All times are GMT
Page 1 of 1

 