International sales DesignBuilder USA DesignBuilder China DesignBuilder Australia DesignBuilder France DesignBuilder Mexico DesignBuilder Portugal DesignBuilder Italy DesignBuilder South Africa DesignBuilder Brazil DesignBuilder Japan DesignBuilder Spain DesignBuilder India DesignBuilder Chile DesignBuilder Czech Replublic, Poland, Hungary, Slovakia DesignBuilder Israel DesignBuilder Greece DesignBuilder South East Asia DesignBuilder Iran DesignBuilder Germany
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Convergence problem

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD
View previous topic :: View next topic  
Author Message
matrix



Posts: 13
PostPosted: Fri Apr 27, 2012 3:11 pm    Post subject: Convergence problem Reply with quote

Hi,
I tried to do a CFD simulation, in which there are some supply diffusers on the ceiling and on internal partitions and some extract grilles on the internal partitions that delimit the room.
After checking the in/out fluxes balance, I started the CFD simulation and after thousands iterations every Residual quantity (x/y/z velocity, turbolence KE, turbolence Dissipation...) converges, except Mass.
I've just tried changing time step, relaxation factors... and also using an higher number of cells, but the Mass doesn't converge.
I don't care about thermal profile, but only the velocity vectors in order to try to understand the air flow route.
Attached you can find the .dbs file.
Thank you for helping me.



Simulazione LAF.dsb
 Description:

Download
 Filename:  Simulazione LAF.dsb
 Filesize:  3.25 MB
 Downloaded:  705 Time(s)

Back to top
View user's profile Send private message
Steve Potter



Posts: 614
Location: newcastle
PostPosted: Fri May 04, 2012 9:12 am    Post subject: Reply with quote

Hi,

The problem with your model is that many of the supply and extract edges coincide with the parent surface edges which can cause the air flow to become 'stalled' or 'locked' at the corners of the domain resulting in the mass source residual failing to fall below a minimum level. If you redraw the supply and extract boundaries ensuring a distance of at least 0.1m between the boundary and parent surface edges (as illustrated), you should find that the mass source will continue to fall.

We will add a comment to the on-line help so that others will hopefully not run into the same problem.

Regards,

Steve



BoundaryEdges.png
 Description:
 Filesize:  13.88 KB
 Viewed:  7135 Time(s)

BoundaryEdges.png


Back to top
View user's profile Send private message
matrix



Posts: 13
PostPosted: Wed May 09, 2012 10:16 am    Post subject: Reply with quote

Hi,
I tried to do simulations after changing extract grilles and supply boundaries as you said, but the problem concerning Mass convergence is still present.
Attached the relevant file .dbs.
Thanks.
Regards.



Simulazione LAF portate soffitto variate.dsb
 Description:

Download
 Filename:  Simulazione LAF portate soffitto variate.dsb
 Filesize:  3.4 MB
 Downloaded:  693 Time(s)

Back to top
View user's profile Send private message
Steve Potter



Posts: 614
Location: newcastle
PostPosted: Wed May 09, 2012 2:57 pm    Post subject: Reply with quote

Hi,

There is still one small supply boundary on the ceiling which is causing a problem because it is too close to the parent surface edge. If you delete this boundary and incorporate the flow rate within one of the adjacent supply boundaries, you should find that the mass source then continues to reduce.

I have attached a screenshot that highlights the location of the problem supply boundary.

Regards,

Steve



ConflictingSupply.png
 Description:
Supply boundary too close to parent surface edge
 Filesize:  32.3 KB
 Viewed:  7005 Time(s)

ConflictingSupply.png


Back to top
View user's profile Send private message
matrix



Posts: 13
PostPosted: Tue May 15, 2012 9:42 am    Post subject: Reply with quote

Hi,
I tried again following your suggestion but the mass still doesn't converge. Furthermore

it seems that also the velocity components fluctuate.
I saw that even if after 10'000 iterations the quantities continued to fluctuate.

Regards.



Simulazione LAF portate soffitto variate.dsb
 Description:

Download
 Filename:  Simulazione LAF portate soffitto variate.dsb
 Filesize:  1.6 MB
 Downloaded:  660 Time(s)

Back to top
View user's profile Send private message
Steve Potter



Posts: 614
Location: newcastle
PostPosted: Sat May 19, 2012 3:00 pm    Post subject: Reply with quote

Yes, there is still a mass convergence problem with your model which appears to be caused by the adjacent extract boundaries on the surface indicated on the attached screenshot. While we investigate the underlying reason for this, a workaround is to combine these extracts into a single extract. Generally speaking, it is better to avoid placing ventilation boundaries hard up against each other.

After making this modification, you should find that the solution converges in a relatively stable fashion for coarser grids (> 0.3m grid spacing) but for finer grids (< 0.2m grid spacing), the solution becomes somewhat unstable with high oscillations in the residuals. However, if you use a small grid spacing, you can improve the stability by reducing the velocity false time steps to a value of around 0.005 and you should find that the solution then stabilises after around 200-300 iterations.

Hope this is of help.

Steve



Extracts.png
 Description:
Combine extracts
 Filesize:  29.47 KB
 Viewed:  6713 Time(s)

Extracts.png


Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B