| View previous topic :: View next topic |
| Author |
Message |
rahmiandarini
Posts: 56
|
Posted: Thu May 15, 2008 9:54 am Post subject: |
|
|
Hi Arturo,
Thanks for the idea. Yesterday I also thought that it could be done like that. But, still I get stuck with the initial point.
1. Which comfort conditioning temperature should I use for the first step using Slab? I have 2 storeys building, and there is a hole (I assume for staircase). Is it ground floor, or first floor? or take for whole building?
2. In Slab program, there is option of DEEP temp, which temperature is this? is it temperature the I got form CalcSoilSurfTemp?
3. In DB, I have possibility to use separate construction and add ground construction layers to surfaces in contact with ground, in your suggestion, for the first option (Conditioned building), do I need to do this as there is SLAB DEPTH in Slab Program?
Thanks,
Rahmi
|
|
| Back to top |
|
 |
lklawrie
Posts: 189
|
Posted: Thu May 15, 2008 12:21 pm Post subject: |
|
|
Ground OSC Example File:
The slab program determines and produces monthly temperatures corresponding to the average outside temperature of the slab, the outside temperature of the core region, and the outside temperature of the perimeter region. Generally most users input the average outside slab temperatures in the GroundTemperatures object, but if a user wants to use both the core temperature and the perimeter temperature, the slab surface must be divided into appropriate regions, and one of the region's temperatures need to be supplied using the OtherSideCoefficients object. The Slab program produces the needed objects but they have to be named to fit the model. The example file just demonstrates the use of the OtherSideCoefficients object and the corresponding monthly temperature values in a CompactSchedule object. check the outside surface temperatures of the South wall to see that the temperatures from the CompactSchedule object were applied to the outside of the surface.
_________________ Linda
EnergyPlus Development Team |
|
| Back to top |
|
 |
AOG

Posts: 172
|
Posted: Sat May 17, 2008 3:03 am Post subject: |
|
|
Hi all,
About Rahmi questions:
1. I used theoretical comfort temperatures for each month calculated with a simply formula, e.g. thermal neutrality (Tn = 17.6 + 0.31 Tave).
2. If you are referring to TDEEPin, it is the fixed temperature you can set to the lower surface of the model, if the field FIXBC: is the lower boundary at a fixed temperature is set as TRUE (you can define the deep of model lower surface in the field ZCLEARANCE: Depth of region below slab, in the EquivAutoGrid object). I think you can estimate this temperature from .stat file related whit your .epw file, if it provides calculated undisturbed ground temperatures at least for 4m deep, or use a value near to average annual dry bulb temperature for the site. Otherwise, as I understand help document, if you set FIXBC as FALSE the program will calculate by itself an undisturbed temperature profile (please Linda tell me if I’m wrong).
3. Well, I understand this issue as follow. In DesignBuilder ground monthly temperature applies for outside surface of every surface adjacent to ground. Then, if you are using combined constructions, ground monthly temperature applies for outside surface of ground floor slab. If you use separated construction, and add a ground construction layer, ground monthly temperature applies for outside surface of this layer. So, in the last case, depth at which ground monthly temperature applies will depend on the thickness of the added layer. Said this, I think values obtained within Slab are more accuracy with first option (combined construction) or with the second one if don’t add any layer.
Daniel:
It’s really nice to meet a Mexican colleague in this forum. You can contact me through my web site (see it in my profile) or directly at arturo at sol-arq dot com. It will be great to collaborate in such study. Un gran saludo desde Chihuahua.
Regards,
Arturo
|
|
| Back to top |
|
 |
andfranz
Posts: 105
|
Posted: Fri Nov 25, 2011 12:57 pm Post subject: |
|
|
I know that the subject is dealt with by the Annex D (Application to dynamic simulation programmes) of the European technical standard EN ISO 13370:2008 "Thermal performance of buildings - Heat transfer via the ground - Calculation methods", but I have never used it…
Has someone got more experience?
With Regards
|
|
| Back to top |
|
 |
andfranz
Posts: 105
|
Posted: Thu May 17, 2012 7:42 am Post subject: |
|
|
| andfranz wrote: | I know that the subject is dealt with by the Annex D (Application to dynamic simulation programmes) of the European technical standard EN ISO 13370:2008 "Thermal performance of buildings - Heat transfer via the ground - Calculation methods", but I have never used it…
Has someone got more experience?
With Regards |
Now I used that technical standard, but I got strange results (e.g. during the winter, in an Alpine valley, the results say that the ground temperature is very close to the internal temperature, and the internal space is heated...).
If you are interested in knowing details, let me know.
Two scientists advice me to read the following publications:
http://www.nrel.gov/docs/fy09osti/45742.pdf (summary conference paper)
http://www.nrel.gov/docs/fy08osti/43388.pdf
|
|
| Back to top |
|
 |
andfranz
Posts: 105
|
Posted: Thu May 17, 2012 7:50 am Post subject: |
|
|
| Andy Tindale wrote: | I've thought for some time that it should be possible to provide 'good enough' estimates of monthly ground temperature for input to E+ using a simple rule of thumb. We could set up an interpolation between 2 cases:
1. Undisturbed ground temperatures from epw file
2. Inside temperature - 2
For infinitely large buildings the temperature will be 2 and for infinitely small buildings it is 1. Other buildings lie somewhere between 1 and 2, the interpolation being done using the ratio of ground adjacent perimeter to floor area as a measure of building impact on ground temperature.
It could be an interesting MSC research project to derive a correlation from running detailed simulations of many different sized and shaped building footprints.
Andy |
I think that the interpolation between 2 cases:
1. Undisturbed ground temperatures from epw file
2. Inside temperature
would be the best solution, but I don't understand what equation we could use to interpolate.
In the International System of Units the ratio of ground adjacent perimeter to floor area is
m / m^2 = 1/m
therefore it is not a dimensionless number. Probably the best solution would be the use of a finite element method software, but a faster solution would be very useful.
Best Regards
|
|
| Back to top |
|
 |
jean marais
Posts: 95
|
Posted: Tue May 22, 2012 2:10 pm Post subject: |
|
|
Just a thought...
I've done this for a project in Germany. Somethings to think about are
1) Where is the ground water level...this will have the "deep ground temperature"
2) A good reason that the temp under the slab is different is that it is not "exposed" to the ODA environment at the top and has no wind or radiation effects on it as does the gound in the cow field.
3) The slab thickness has a big effect on the outside temp of the slab.
4) The Slab program does a good job. It is a 3d FDM program and even takes into account shading from the height of the building on the ground next to the building.
The cyclic average inside temperature variation is also accounted for. Because the slab has a certain thermal "inertia" the average room temp is good enough for the simulation.
|
|
| Back to top |
|
 |
jefh25
Posts: 2
|
Posted: Tue May 22, 2012 9:32 pm Post subject: |
|
|
The slab program is the best option, look for the tutorial named: "leture 24 ground heat transfer".
In this presentation you will find and example, and an easy explanation of how to use the slab program.
I will try to attach the document.
| Description: |
|
 Download |
| Filename: |
Lecture 24 Ground Heat Transfer.ppt |
| Filesize: |
224.5 KB |
| Downloaded: |
123 Time(s) |
|
|
| Back to top |
|
 |
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum You cannot attach files in this forum You can download files in this forum
|
Powered by p h p B B
|