International sales DesignBuilder USA DesignBuilder China DesignBuilder Australia DesignBuilder France DesignBuilder Mexico DesignBuilder Portugal DesignBuilder Italy DesignBuilder South Africa DesignBuilder Brazil DesignBuilder Japan DesignBuilder Spain DesignBuilder India DesignBuilder Chile DesignBuilder Czech Replublic, Poland, Hungary, Slovakia DesignBuilder Israel DesignBuilder Greece DesignBuilder South East Asia DesignBuilder Iran DesignBuilder Germany
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

polycarbonate twin-wall sheet

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus General
View previous topic :: View next topic  
Author Message
pantakrator78



Posts: 26
PostPosted: Fri Jun 15, 2012 10:03 am    Post subject: polycarbonate twin-wall sheet Reply with quote

Hi there,

I couldnt find polycarbonate twin-wall sheet in the material library. Therefore I tried to creat it bymyself:
polycarbonate 2 mm / air 14mm / polycarbonate 2mm
nevertheless, such sheets have also vertical dividers in every few centimeters.
Do u have any idea how to model a polycarbonate twin-wall sheet?

Regards

panta
Back to top
View user's profile Send private message
Andy Tindale



Posts: 2619
Location: Stroud
PostPosted: Mon Jun 18, 2012 5:40 pm    Post subject: Reply with quote

Panta,

Probably the easiest way would be to find total glazing SHGC, visible transmittance and U-value and use the Simple definition method. As you say twin wall polycarbonate has a complex structure which would not suit the layer by layer definition approach.

Andy
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus General All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B