|
|
| View previous topic :: View next topic |
| Author |
Message |
koen.govers
Posts: 80
|
Posted: Wed Mar 19, 2008 11:45 am Post subject: Results System Fans energy |
|
|
Hi Andy,
I have completed a simulation of an office building and get strange results for the fans energy consumption.
If I compare the DB results with manual calulation I get a 4-5 error factor.
- DB result: System Fans: 521.710 kWh/year
- Manual calculation (see used values below): 118.261 kWh/year.
the (by hour simulation) results of total fresh air (ach) seem right(schedule and flow) but the fan power isn't.
I'm working with:
Compact HVAC,
unitary single zone,
System Availability: Scheduled with occupancy,
Min AHU Outside Air RequirementScheduled with occupancy,
Fan operation Mode: Continuous,
Pressure rise: 1900 Pa,
Total efficiency: 68.
Outside aid definition method: By zone
The total ventilation flow should be around 19.000 m³/h (manual calculation).
Schedule: 15 h/day, 260 days/year.
Do you have an idea of what the problem could be?
Thanks,
Koen |
|
| Back to top |
|
 |
koen.govers
Posts: 80
|
Posted: Wed Mar 19, 2008 11:46 am Post subject: |
|
|
Andy,
I've just sent you the files by e-mail.
Koen |
|
| Back to top |
|
 |
Andy Tindale

Posts: 1198 Location: Stroud |
Posted: Thu Mar 20, 2008 1:19 am Post subject: |
|
|
Remember that fan airflow is the supply flow rate which may include recirculated air in addition to the outside air flow rate.
If this does not explain it, could you send details of your calculation for fan energy so we can compare it with the E+ results? I saw the data on the spreadsheet you sent but didn't understand the steps. It would help if you could translate the headings. |
|
| Back to top |
|
 |
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum You cannot attach files in this forum You can download files in this forum
|
Powered by p h p B B
|
|