Doubts with the compact schedule

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation
View previous topic :: View next topic  
Author Message
llyces1985



Posts: 32
PostPosted: Mon Mar 31, 2008 1:11 pm    Post subject: Doubts with the compact schedule Reply with quote

Hi,

In the help file in DB about 'Defining setpoint temperature schedules', it says, if the valume=0 ,Equipment is off,
> 0.5, Equipment is controlled using the main temperature setpoint data (Activity tab),
0 < Value <= 0.5, Equipment is controlled using the setback temperature setpoint data (Activity tab),


but, in the Schedule template, I find that:

SCHEDULE:COMPACT,
SportCtr_CellOff_Occ,
Fraction,
Through: 31 Dec,
For: Weekdays SummerDesignDay,
Until: 07:00, 0,
Until: 08:00, 0.1,
Until: 09:00, 0.2,
Until: 10:00, 0.5,
Until: 12:00, 1,
Until: 14:00, 0.5,
Until: 17:00, 1,
Until: 18:00, 0.25,
Until: 19:00, 0.2,
Until: 21:00, 0.1,
Until: 22:00, 0.05,
Until: 24:00, 0,
...
what are the 0.05,0.1,0.2,and 0.25 meanings? If they mean that the equipment is 'controlled using the setback temperature setpoint data', why not set the valume of 0.5 between the time of 07:00 and 10:00? Or they have other meanings?

And another compact template:

SCHEDULE:COMPACT,
SportCtr_Changing_Occ,
Fraction,
Through: 31 Dec,
For: Weekdays SummerDesignDay,
Until: 08:00, 0,
Until: 09:00, 0.25,
Until: 16:00, 0.75,
Until: 18:00, 0.5,
Until: 20:00, 0.75,
Until: 22:00, 0.25,
Until: 24:00, 0,
...
I can not catch up with it! Could I define it like this:

SCHEDULE:COMPACT,
SportCtr_Changing_Occ,
Fraction,
Through: 31 Dec,
For: Weekdays SummerDesignDay,
Until: 08:00, 0,
Until: 09:00, 0.5,
Until: 16:00, 1,
Until: 18:00, 0.5,
Until: 20:00, 1,
Until: 22:00, 0.5,
Until: 24:00, 0,
...
or not? If yes, I think it is simpler than the former one. If not, why? Thanks a lot!
All the best,

Esong
Back to top
View user's profile Send private message MSN Messenger
Laurent_Support



Posts: 292
Location: Vincennes
PostPosted: Mon Mar 31, 2008 2:29 pm    Post subject: Reply with quote

Hello,

The Help is correct about controlling setpoint temperature.

The schedule you paste are ASHRAE data, independent from EnergyPlus, DesignBuilder softwares.
I understand values could disappoint you but it works as intended and will allow more accurate settings in the future.

Regards,
Laurent
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum