|
|
| View previous topic :: View next topic |
| Author |
Message |
hannes
Posts: 17 Location: Gent |
Posted: Tue May 06, 2008 9:52 am Post subject: glazing U-value |
|
|
Hello,
I'm modelling a building with glazing I selected from the DB database (outerpane SGG Climaplus Cool-lite KN155 and innerpane SGG Planilux separated with Argon 16mm).
The calculated SGGC and light tramsmission factors correspond quite well with the data provided by SGG.
It's the calculated ASHRAE U-value (2.551 W/m²K) that is different from the provided EN673 value (1,4 W/m²K), which has an impact on the calculated heating load.
What is the explanation for this and why is the possibility left open to change this calculated U-value?
Besides, changing this U-value doesn't affect the heating design calculation.
Regards,
Hannes
Technum NV |
|
| Back to top |
|
 |
bhandari
Posts: 78
|
Posted: Tue May 06, 2008 1:51 pm Post subject: |
|
|
Hannes,
The difference probably is due the different heat transfer coefficients used in the calculations of U Factor. For example, EN673 uses exterior heat transfer coefficient - ho=23 W/m2K while ASHRAE uses ho= (26 W/m2K + radiative heat transfer coefficient) which would approximately be 30W/m2K. The value reported by manufacture are generally based on ASHRAE heat transfer coefficients.
Please note that E+ will remove the heat transfer coefficients used for U factor calculation and calculate the heat transfer coefficients based on wind velocity and surface roughness. So, this is not left to open, as in both the cases (ASHRAE vs EN673), E+ will use the same glazing properties for the calculations.
regards,
Mahabir |
|
| Back to top |
|
 |
hannes
Posts: 17 Location: Gent |
Posted: Wed May 07, 2008 7:56 am Post subject: |
|
|
Thank you,
I think the difference is due to the fact the coating on the outermost pane is modelled on the outside (side1). In Window5 there is a possibility to flip the pane to have the coating on the right side. Is this possible in DB too?
Regards, Hannes |
|
| Back to top |
|
 |
Florent
Posts: 2
|
Posted: Wed May 07, 2008 11:07 am Post subject: |
|
|
You can create a new environnemental condition in Window5 with a 15K Outside/Inside deltaT like the EN673.
I think it will be useful to have this possibility in DB.
Regards,
Florent |
|
| Back to top |
|
 |
AJ Lester
Posts: 65 Location: Auckland |
Posted: Wed May 07, 2008 8:39 pm Post subject: |
|
|
Hello Hannes,
At present I believe that DB does not have the capability to handle flipping panes of glass or demonstrating which side of the glass a coating is on - it is on the development list for a future version.
See this response from Andy to an earlier question on a similar topic:
http://www.designbuilder.co.uk/component/option,com_forum/Itemid,25/page,viewtopic/t,1127/
So hopefully it shouldn't be too long before we see this functionality in DB!
All the best,
Andrew |
|
| Back to top |
|
 |
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum You cannot attach files in this forum You can download files in this forum
|
Powered by p h p B B
|
|