International sales & support  DesignBuilder USA website  DesignBuilder Italy website  DesignBuilder Australia website  DesignBuilder France website  DesignBuilder Mexico website  DesignBuilder Portugal website
Home

Login

Username

Password

Remember me
Lost Password or Username?
No account yet? Register
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

downloading version 1.4 plus questions

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation
View previous topic :: View next topic  
Author Message
ecoperfil



Posts: 9
PostPosted: Mon May 12, 2008 6:03 pm    Post subject: downloading version 1.4 plus questions Reply with quote

Hello,

I'm working with version 1.3 and I'm facing some problems, namely the inability to simulate (the model does not finish runnning, giving out severe errors) a naturally ventilated underground car park. This model, however runs normally in version 1.4 (my collegue's trial version). However, I just tried to download it but the page won't open, so I'm a bit desperate. I have a purchaced DB key.

In the v1.4 program, I'm experiencing problems with the minimum outside air requirements, when using the VAV HVAC system. While in v1.3, in the Activity tab, the minimum fresh air requirement was only defined in l/s.oc (and it was ok with me), now it also presents a value for mechanical ventilation, in l/s.m2. However, if I calculate my fresh air needs in l/s.m2 (during the day, in winter, all ventilation is mechanical in the building I'm simulating), the results don't give me the minimum air changes per hour I need to supply in each zone. This is rather stressing, since I though the program used the minimum fresh air requirements in l/s.oc, simply multiplying it by the number of occupants (derived from the occupant density and the zone area) and gave out the minimum air changes per hour. Please help me solving this problem.

Best regards,

André Coelho
Portugal
Back to top
View user's profile Send private message
Laurent_Support



Posts: 275
Location: Vincennes
PostPosted: Tue May 13, 2008 7:44 am    Post subject: Reply with quote

Hello André,

I hope you succeed to downloading 1.4 (may be a site problem).

In v1.4, new options appear but the ACH in l/s.oc still exists. You can select the way the fresh air is calculated in the HVAC tab under Air distribution.

You will find many options but the 'per person' calculation run fine.

Regards,
Laurent
Back to top
View user's profile Send private message Visit poster's website
ecoperfil



Posts: 9
PostPosted: Tue May 13, 2008 3:35 pm    Post subject: minimum fresh air entry parameters Reply with quote

Dear Laurent,

Thank you. I finally completed the v1.4 download.

The minimum fresh air attribute I was referring to was on the Activity tab, right under the Minimum Fresh Air tab entry in l/s.oc. What I don´t understand is which parameter has priority (fresh air in l/s.oc or Mech vent per area, in l/s.m2), or if they are completely separated.

Best regards,

André C.
Back to top
View user's profile Send private message
Laurent_Support



Posts: 275
Location: Vincennes
PostPosted: Wed May 14, 2008 9:54 am    Post subject: Reply with quote

Hi,

There is no priority. Depending on the Air Distribution Calculation mode you chose, these parameters will be taken into account or not.

For instance, if you select 'Per person', the l/s.m2 you see in the Activity tab is not used.
On the contrary, if you select 'Per area', the l/s.oc from Activity tab is not used.
You can also select option to sum the both or have the max.
This is help topic about all options:
http://www.designbuilder.co.uk/programhelp/outside_air.htm

Nice features to play with, isn't it?

Laurent
Back to top
View user's profile Send private message Visit poster's website
ecoperfil



Posts: 9
PostPosted: Fri May 16, 2008 11:22 am    Post subject: minimum fresh air options in v1.4 Reply with quote

Dear Laurent,

Yes, thanks. It's clear now. However, to avoid confusion, maybe one of the options in the Minimum Fresh Air tab of the Activity tab coulb be "blocked" or "unavailable", depending on the selection of the minimum fresh air method selected on the HVAC tab.

Nice feature, though, I agree. The more options, the more flexible. Smile

Best regards,

André C.
Ecoperfil
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-6.