lklawrie
Posts: 77
|
Posted: Wed Jun 11, 2008 2:44 pm Post subject: |
|
|
Yes, would like to know if this is still a problem with the latest ExpandObjects/DB version (even if beta version, if possible). Would like to track it down for you.
_________________ Linda
EnergyPlus Development Team |
|
| Back to top |
|
 |
Andy Tindale

Posts: 1205 Location: Stroud |
Posted: Fri Jun 13, 2008 12:24 pm Post subject: |
|
|
Below is a new version of ExpandObjects for EnergyPlus v.2.2 supplied by Linda Lawrie. Please unzip the exe file and copy to the EnergyPlus folder (File > Folders > EnergyPlus folder) to see if it helps solve this problem.
Andy
| Description: |
| New ExpandObjects for EnergyPlus v.2.2. Unzip and copy ExpandObjects.exe to EnergyPlus folder |
|
 Download |
| Filename: |
ExpandObjects.zip |
| Filesize: |
327.47 KB |
| Downloaded: |
393 Time(s) |
|
|
| Back to top |
|
 |
Energyy
Posts: 1
|
Posted: Fri Jul 11, 2008 12:06 pm Post subject: Energy |
|
|
I'm a new spanish user of DB. I have the same problem with the "Error expanding compact HVAC descriptions".
You have solved this problem with possible solutions earlier???? I have tried these solutions and the problem continues.
I need solve this question early.
I will appreciate an answer.
Thanks a lot!!!
Energy
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1205 Location: Stroud |
Posted: Fri Jul 11, 2008 12:20 pm Post subject: |
|
|
Energy,
We will need your help to solve this problem!
Could you send us a diagnostics.log file generated immediately after a failed compact hvac simulation?
Click on Tools menu and then 'Show log file' then click on the 'Send to DesignBuilder support' button. This uploads the log file to our website - please also let me know when you have done this so we can find your log and look into the problem.
Andy
|
|
| Back to top |
|
 |
nuria.quince
Posts: 1
|
Posted: Fri Jul 11, 2008 3:22 pm Post subject: Reply for Andy |
|
|
Hi Andy!
Thank you very much for your quick response.
I've already sent to you the .log file and also the .dsb file in order you can solve this problem.
Thanks!
Energy
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1205 Location: Stroud |
Posted: Wed Aug 06, 2008 6:37 pm Post subject: |
|
|
We may have found a fix for this problem for some computers and will be releasing a new beta (1.6.3 or later) in next few days. If you have been experiencing this problem with Compact HVAC, I would be very grateful if you could give 1.6.3 (or later) a try when it becomes available to see if it fixes it more generally.
Thanks,
Andy
|
|
| Back to top |
|
 |
hallik
Posts: 14
|
Posted: Thu Oct 02, 2008 12:55 pm Post subject: A new try with 1.6.9.003, but no luck |
|
|
Hi Andy,
I finally got a chance to upgrade to the latest DB release (1.6.9.003) and had some spare time to fiddle with this problem again. So I changed program options to use the recommended internal dll (2.2.0.025) for calculation, but the "error expanding compact HVAC..." message keeps popping up. I reran those commands you recommended in your 17 Dec 2007 17:42 post on the first page of this topic (ie. manually check in.idf presence and run ExpandObject from commandline) and it seems that in.idf is generated before the "error expanding compact HVAC..." message and manually executing ExpandObjects from command line generates expanded.idf with no errors. So it is a little progress compared with the previous attempts, but still not working through DB interface as expected. The last few dozens of lines in the log file is as follows:
| Code: | Energy+.idd - fn C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\Energy+.idd
Energy+.idd - version 2.2.0.025
EnergyPlus installed and up-to-date
EnergyPlus license check pass
RunEP 1
C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\in.idf exists (1) : True
RunEP Copied C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\in.idf to C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\compact.idf
C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\in.idf exists (2) : True
C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\in.idf exists (3) : True
ShellAndWaitForTermination BatchFileContent:
C:
cd "\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\"
erase marker
Call ExpandObjects.exe
copy "dbrunep.bat" marker
ShellAndWaitForTermination sStdOut:
Error expanding compact HVAC descriptions
C:\Documents and Settings\hallik\Local Settings\Application Data\DesignBuilder\EnergyPlus\Expanded.idf not generated
Please contact DesignBuilder support
RunEP Exit
Ended SSCalcOptions.CalcSingleBuildingNoDialog |
So can I try to tweak something to help to solve the issue? I have some spare time to devote next couple of days.
All the best,
Jaanus
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1205 Location: Stroud |
Posted: Thu Oct 02, 2008 4:46 pm Post subject: |
|
|
Hi Januus,
OK here's the latest advice on getting past this problem. Go to Program options dialog and on the Developer tab change the Shell option from 1-API-pipe to 5-Basic. This new 'Basic' option provides an new 'low-tech' way to launch the ExpandObject.exe program and the workaround has helped get Compact HVAC working for others with the problem.
Please let us know how you get on.
Andy
|
|
| Back to top |
|
 |
hallik
Posts: 14
|
Posted: Fri Oct 03, 2008 8:04 am Post subject: |
|
|
Worked like a charm. Thank you Andy.
Jaanus
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1205 Location: Stroud |
Posted: Fri Oct 03, 2008 8:50 am Post subject: |
|
|
That's good news.
Since this fix seems to be successful we'll change DB so that it automatically uses this method if the standard API-Pipe method fails.
Thanks for letting us know.
Andy
|
|
| Back to top |
|
 |
|