International sales & support  DesignBuilder USA website  DesignBuilder Italy website  DesignBuilder Australia website  DesignBuilder France website  DesignBuilder Mexico website  DesignBuilder Portugal website
Home

Login

Username

Password

Remember me
Lost Password or Username?
No account yet? Register
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Heat loss through walls in summer

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> DesignBuilder Support
View previous topic :: View next topic  
Author Message
francoisgferreira



Posts: 9
PostPosted: Wed Jul 09, 2008 9:19 am    Post subject: Heat loss through walls in summer Reply with quote

Hallo

I have att my program to this message, can you please conferm why the walls Groundfloor- Strong Room 1 gives a negative value for cooling design. The outside temp is bigger than that of the room, should this value not be positive?

Regard
Francois



Kimberley Archieves.dsb
 Description:

Download
 Filename:  Kimberley Archieves.dsb
 Filesize:  1.41 MB
 Downloaded:  213 Time(s)

Back to top
View user's profile Send private message
Laurent_Support



Posts: 275
Location: Vincennes
PostPosted: Wed Jul 09, 2008 1:27 pm    Post subject: Reply with quote

Hello Francois,

You've got a negative value for your floor is adjacent to ground and ground does not have the same temperature as the outside air.

If you click on Site level and watch to the location tab > Site details > Ground temperatures, you will notice your ground is at 14°C every month (so less than 24° in the room).

You should change them to more realistic values.

Regards,

_________________
Laurent
Back to top
View user's profile Send private message Visit poster's website
francoisgferreira



Posts: 9
PostPosted: Wed Jul 09, 2008 1:57 pm    Post subject: Reply with quote

You mis-understood the question, please look at the zone "Groundfloor- Strong Room 1", there my walls give the negative value...

Regard Francois
Back to top
View user's profile Send private message
Laurent_Support



Posts: 275
Location: Vincennes
PostPosted: Thu Jul 10, 2008 3:23 pm    Post subject: Reply with quote

Sorry,

I have a look to the wall now Smile
The reason why walls heat flow is negative is due to the fact that outside air is always inferior to zone temperature. So heat is always going outward.

Regards,

_________________
Laurent
Back to top
View user's profile Send private message Visit poster's website
francoisgferreira



Posts: 9
PostPosted: Tue Jul 15, 2008 6:38 am    Post subject: Air Temperature and Outside drybulb Reply with quote

I have attached the analysis Results (excel). If I look at the roof load, it is how I expect it to react, if the outside drybulb is lower than the air-temp then the cooling load becomes smaller. If the outside drybulb is higher than the air-temp then the cooling load becomes bigger. This does not happen to the walls. Look at the highlighted colloms in the file.

Regard
Francois



Analysis Results.xls
 Description:

Download
 Filename:  Analysis Results.xls
 Filesize:  47 KB
 Downloaded:  245 Time(s)

Back to top
View user's profile Send private message
Laurent_Support



Posts: 275
Location: Vincennes
PostPosted: Tue Jul 15, 2008 12:02 pm    Post subject: Reply with quote

Hi,

For roof you should have the same results as for walls, ie heat transfer from interior to outside (because outside temperature < internal temperature).

Now, solar radiation heat, some days, the external layer of your roof, increasing the outside air temperature next to the roof. This is why for the roof heat transfer are going from outside to the interior when sun shines a lot.

Regards,

_________________
Laurent
Back to top
View user's profile Send private message Visit poster's website
francoisgferreira



Posts: 9
PostPosted: Tue Jul 15, 2008 1:47 pm    Post subject: Reply with quote

Have you looked at my result???
What you say is true but the results I get does not concure with what you just said. You are not giving me a reason way my walls are gaining energy(adding to the cooling load) at night and release energy(subtracting from the cooling load) at day for summer design. This, as you have mentioned in the previous 2 mail should not happen.
Back to top
View user's profile Send private message
Laurent_Support



Posts: 275
Location: Vincennes
PostPosted: Tue Jul 15, 2008 3:51 pm    Post subject: Reply with quote

Well you may understand I'd rather use the dsb file you posted to know what is your model and settings. An result file is surely interesting but can't help me to answer you.

I apologize if I answer too quickly and I will try to give you better info with this post!
Your wall construction are heavy structure with much thermal mass. Suspecting this create a time phase offset I try a simple brick work + plaster board construction for all walls.
Results shows that heat flow is quicker inverse at morning and night. In my example, wall heat exchange are negative from 02:00 AM till 11:00 AM only.

Regards,

_________________
Laurent
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> DesignBuilder Support All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-6.