Flow Imbalance

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD
View previous topic :: View next topic  
Author Message
mbwaite



Posts: 46
Location: New York, NY
PostPosted: Fri Oct 10, 2008 7:15 pm    Post subject: Flow Imbalance Reply with quote

When trying to run CFD in a simulation of a generic building I get a message in the "CFD Grid Statistics" that there is a "Flow imbalance, Inflow=423.8 CFM, Outflow=0.000 CFM." I'm not sure what would cause this. I get the same message with the same numbers whether I am trying to simulate the entire building or just one floor or zone. I have one zone with 2 CFD boundaries.

I am just beginning to play around with this. Are there plans for a help file, tutorial or other documentation?

Thanks,

Mike
Back to top
View user's profile Send private message
Steve Potter



Posts: 298
Location: newcastle
PostPosted: Sat Oct 11, 2008 9:48 am    Post subject: Reply with quote

Hi Mike,

When you set up ventilation boundary conditions for a model (supply diffusers and extract grilles), you need to ensure that the amount of air supplied to the domain matches the amount of air removed otherwise you will see the flow imbalance error message.

In this case it looks as if you've defined some supply (423.8 cfm) but no extract. You will need to position extracts with a defined flow rate equal to a total of 423.8 cfm.

We will be making the documentation available within the next week or so.

Regards,

Steve
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-8.