lvidal
Posts: 74 Location: Paris |
Posted: Mon Nov 13, 2006 9:46 am Post subject: Temperature control in Simulation options ? |
|
|
Hello again
What means and what's the impact of temperature control (Air temp, operationnal temp, other) new field in the Simulation options ?
Best regards,
Laurent |
|
| Back to top |
|
 |
Andy Tindale

Posts: 2619 Location: Stroud |
Posted: Mon Nov 13, 2006 10:22 am Post subject: |
|
|
Hello Laurent,
The temperature control is the radiant fraction of the thermostat controlling the heating/cooling system.
So if you select 1-Air temperature it is the air temperature that is controlled to the heating setpoint temperature on the activity tab.
If you select 2-Operative temperature then you will find the operative temperature is controlled to the setpoint.
Real thermostats generally sense air more strongly than radiant temperatures but operative temperature control is a useful way to ensure that the building thermal model maintains comfort conditions during the occupied period.
The temperature setpoints on the activity tab generally represent operative temperatures.
Regards,
Andy |
|