Bobby Gilbert



Posts: 20
PostPosted: Sat Mar 29, 2008 2:06 pm    Post subject: Zone heat balance output Reply with quote

In the help system topic "Simulation detailed results" it says...

Note: taken together the Internal gains and the Fabric and ventilation data above give an approximate Zone Heat Balance, i.e. the data represents all of the heat flows into and out of the zone.

Could you explain why this is only approximate? I have done a simulation and over the course of a year the 100m2 house I am modelling in UK weather is 400kwh short of heat to acheive a heat balance over the year. It ends the year at almost the same temperature as it starts the year so this does not appear to be due to it cooling down.

Also, possibly related, there don't appear to be any casual gains for DHW accounted for when DHW is turned on. Are any casual gains included for hot water? if so how do I find how much?

Thanks

Bobby
Back to top
View user's profile Send private message
Andy Tindale



Posts: 1148
Location: Stroud
PostPosted: Sat Mar 29, 2008 3:08 pm    Post subject: Reply with quote

Three inaccuracies in the heat balance spring to mind:

1. The solar gain is not 'solar absorbed by the zone' but rather 'solar transmission through glazing' so this is not useful in the heat balance.

2. More esoteric, a heat balance must be carried out at a particular point in the heat flow network, for example the air point or the 'rad-air/environmental' point. But the fabric heat transfer (Walls, Roof Heat Gain etc) is 'heat flow at the surface', whereas the ventilation gains are to the air point. Strictly speaking it is not correct to add gains through walls to gains from ventilation and this could cause a discrepancy.

3. Start up temperatures throughout the building will be different from end conditions. Over the year this effect should be quite small but will cause a non-zero balance.

You didn't say how big 400kWh was relative to the total heat flow but it does sound like a significant error.

There may also be other reasons I haven't thought of.

Andy
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-6.