DB out put and cooling energy from E+ ABUPS

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> DesignBuilder Support
View previous topic :: View next topic  
Author Message
lee68



Posts: 6
PostPosted: Thu Apr 24, 2008 9:55 pm    Post subject: DB out put and cooling energy from E+ ABUPS Reply with quote

Dear Team and other experienced members,
I need some help in correlating the results between E+ and Designbuilder. The E+ results for annual cooling and heating energy (from the report ABUPS) are way higher than DB Chiller (electricity) results. I read the description - calculation of Designbuilder output from EnergyPlus report variable but still could not find the relation between E+ ABUPS cooling energy and chiller (electricity). What exactly is the Cooling Load corresponding to the Cooling energy consumption of ABUPS - which I can divide by COP. Or, in other words what is DB equivalent of total annual cooling energy, if any. Which cooling energy (or heating energy) I should use as my output. Any example would be greatly appreciated. I look forward to hearing from the experts..

The heating/cooling load from the heating/cooling design also do not exactly match with loads in .eio file..

thanks a ton,
John
Back to top
View user's profile Send private message
lee68



Posts: 6
PostPosted: Thu May 01, 2008 1:40 pm    Post subject: Reply with quote

Hello there !!
I have not received any response Sad
John...
Back to top
View user's profile Send private message
Andy Tindale



Posts: 1026
Location: Stroud
PostPosted: Sat May 03, 2008 11:58 am    Post subject: Reply with quote

Hello John,

The first step is to check the help page that explains how DB calculates the results data it displays from E+ eso output data.

http://www.designbuilder.co.uk/programhelp/calculation_of_designbuilder_output_from_energyplus_report_variables.htm

Bear in mind that DB calculates plant energy consumption internally based on heating and cooling coil loads in the E+ eso output file. The data in the ABUPS report will use different boiler and chiller CoP values and does not include distribution losses included by DB.

Andy
Back to top
View user's profile Send private message Visit poster's website
lee68



Posts: 6
PostPosted: Mon May 05, 2008 4:42 pm    Post subject: Reply with quote

Andy,
Thanks for the clarification. It is a bit clear to me
though I would rephrase the question here - what would be the equivalent variables for Chiller (Electricity) and Heat generation (Gas) from .eso reort?

I am also not sure what do you mean by "The data in the ABUPS report will use different boiler and chiller CoP values .... " Does it mean that these values of COPs are different than the one I enter under HVAC tab? If yes, where does that COP come from?

You guys are awesome in responding to the questions. I truely apprecaite your help..
John.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> DesignBuilder Support All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-6.