Posted: Wed May 28, 2008 6:06 pm Post subject: Problem with solar gains results |
|
|
Hello,
the problem is getting very big solar heat balance differences in simulation results between DB and PHPP2007 (Passive house planning package, using EN 13790 monthly method).
Tried several things but couldnīt find a mistake or a reason for the differences, also havenīt experienced smth like this before using DB.
Total solar heat gains DB: approx. 17000 kWh (solar gains exterior windows - glazing)
Total solar heat gains PHPP: approx. - 8000 kWh. (solar gains - transmission losses)
In both cases the frame values are included.
The difference comes from much bigger transmission losses according to PHPP2007, although the results should be comparable.
Since the building has big air spaces through several floors I also tried different solar shading calcs but that didnīt give that much difference.
If you could find a solution or suggest something it would be great.
Best Regs,
Ago Siiner
Ps. I added the file as attachment
| Description: |
|
 Download |
| Filename: |
Lavazza_operative temperature.dsb |
| Filesize: |
1.72 MB |
| Downloaded: |
219 Time(s) |
|
|
| Back to top |
|
 |
Laurent_Support
Posts: 275 Location: Vincennes |
Posted: Fri May 30, 2008 12:11 pm Post subject: |
|
|
Hello Ago,
I run your model and get these results:
| Code: | Month Glazing Solar gains
kWh kWh
01 -3045,4 423,69
02 -2527,13 1388,08
03 -2029,76 2002,27
04 -905,64 3118,4
05 -66,73 4119,69
06 118,83 3943,75
07 141,8 3988,16
08 -297,09 3203,61
09 -716,96 2067,85
10 -1564,45 1248,46
11 -2675,19 347,32
12 -3090,19 123,96
Total -16657,92 25975,23 |
So if I add both values, my glazing balance is positive.
On the other hand, I don't know if PHPP2007 takes into account yearly solar gains or only winter months gains.
I say that for, if you sum solar gains for months 10 to 04, you have only 8,6 MWh.
Glazing losses - winter solar gains = 16,6 - 8,6 = 8 MWh.
So I wonder if the problem between PHPP and DesignBuilder wouldn't be only a period summation to well define.
I will be interested in knowing what PHPP solar gains are used (all year or not) for I begin to work with it also! Thank you.
Regards,
Laurent
|
|
| Back to top |
|
 |
agosiiner
Posts: 2
|
Posted: Mon Jun 02, 2008 2:36 pm Post subject: |
|
|
Hello,
thank You for the reply.
I used the yearly values from PHPP (monthly method. otherwise, yes, it sums up only the gains and losses during the heating period). So the problem is elsewhere.
I also think I found the problem. If I check the input file of E+ i cannot find the U -values for the window frames anywhere, I only found the glazing U-value and dimensions. When I calculated the average U-value of the windows and made the calculation in DB without window frames using the average U-value of the glazing the results are starting to look similar.
Maybe You can check why is it so?
Best Regs,
Ago
|
|
| Back to top |
|
 |
Laurent_Support
Posts: 275 Location: Vincennes |
Posted: Wed Jun 04, 2008 9:43 am Post subject: |
|
|
Hello Ago,
U-values are not existing in EnergyPlus idf file for it compute them at each calculation time step.
E+ use :
- materials you define (glazing, frame layouts)
- deltaT temperature at time step (U-value are calculated at precise normative condition)
- convection algorithms taking into account air velocity, surface roughness and radiation ...
And may be I forget other parameters! So U value is changing during simulation.
Of course, U-value will turn around the mean U-value you've got in the literature but this explains why U-value does not exists in the idf.
Regards,
_________________ Laurent |
|