|
|
| View previous topic :: View next topic |
| Author |
Message |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 8:20 am Post subject: Fatal error : opaque surface and window construction(Solved) |
|
|
Hi everyone!
I'm a new french user of DB, and I've try to design a big building. Unfortunatly, when I try to run the simulation, i get the following message :
Program Version,EnergyPlusDLL 2.2.0.025, 10/07/2008 09:57,IDD_Version 2.2.0.025
** Warning ** Requested Time Steps in Hour (2) is less than the suggested minimum of 4.
** Warning ** For a zone sizing run, there must be at least 1 Zone Sizing object input. Zone Sizing Run Control option ignored.
** Warning ** GetGroundTemps: Some values for "GroundTemperatures" fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Severe ** Did not find matching material for construct 1002, missing material = SOLUTION ALGORITHM
** Severe ** Did not find matching material for construct 1002, missing material = CTF
** Severe ** Did not find matching material for construct 1002, missing material = 2000
** Severe ** Nominal U is zero, for construction=1002
** Warning ** Floor Tilt=101.0, much less than expected tilt of 180, for Surface=E_23251_21_0_0, in Zone=23251
** Warning ** Floor Tilt=99.0, much less than expected tilt of 180, for Surface=E_23996_10_0_0, in Zone=23996
** Warning ** Floor Tilt=98.0, much less than expected tilt of 180, for Surface=E_24390_10_0_0, in Zone=24390
** Warning ** Floor Tilt=96.0, much less than expected tilt of 180, for Surface=E_24785_7_0_0, in Zone=24785
** Warning ** Floor Tilt=95.0, much less than expected tilt of 180, for Surface=E_25187_8_0_0, in Zone=25187
** Warning ** Floor Tilt=93.0, much less than expected tilt of 180, for Surface=E_25594_7_0_0, in Zone=25594
** Warning ** Floor Tilt=91.0, much less than expected tilt of 180, for Surface=E_25594_10_0_0, in Zone=25594
** Warning ** Floor Tilt=92.0, much less than expected tilt of 180, for Surface=E_25999_7_0_0, in Zone=25999
** Warning ** Floor Tilt=92.0, much less than expected tilt of 180, for Surface=E_25999_10_0_0, in Zone=25999
** Warning ** Floor Tilt=93.0, much less than expected tilt of 180, for Surface=E_26400_7_0_0, in Zone=26400
** Warning ** Floor Tilt=91.0, much less than expected tilt of 180, for Surface=E_26400_10_0_0, in Zone=26400
** Warning ** Floor Tilt=94.0, much less than expected tilt of 180, for Surface=E_26808_10_0_0, in Zone=26808
** Warning ** Floor Tilt=95.0, much less than expected tilt of 180, for Surface=E_27216_7_0_0, in Zone=27216
** Warning ** Floor Tilt=96.0, much less than expected tilt of 180, for Surface=E_27612_9_0_0, in Zone=27612
** Warning ** Floor Tilt=97.0, much less than expected tilt of 180, for Surface=E_28011_7_0_0, in Zone=28011
** Warning ** Floor Tilt=97.0, much less than expected tilt of 180, for Surface=E_35418_10_0_0, in Zone=35418
** Warning ** Floor Tilt=104.0, much less than expected tilt of 180, for Surface=E_21351_30_0_0, in Zone=21351
** Warning ** Floor Tilt=101.0, much less than expected tilt of 180, for Surface=E_23228_20_0_0, in Zone=21351
** Warning ** Floor Tilt=104.0, much less than expected tilt of 180, for Surface=E_22013_18_0_0, in Zone=21351
** Warning ** Floor Tilt=104.0, much less than expected tilt of 180, for Surface=E_21385_14_0_0, in Zone=21385
** Warning ** Floor Tilt=104.0, much less than expected tilt of 180, for Surface=E_22034_13_0_0, in Zone=21385
** Warning ** Floor Tilt=98.7, much less than expected tilt of 180, for Surface=E_36847_7_0_0, in Zone=36847
** Warning ** Floor Tilt=99.9, much less than expected tilt of 180, for Surface=E_36534_6_0_0, in Zone=36534
** Warning ** Floor Tilt=101.0, much less than expected tilt of 180, for Surface=E_36521_3_0_0, in Zone=36521
** Warning ** Floor Tilt=100.0, much less than expected tilt of 180, for Surface=E_36521_4_0_0, in Zone=36521
** Severe ** GetHTSubSurfaceData: Surface W_23251_19_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_23996_7_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_24390_7_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_24785_10_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_26808_7_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_27216_10_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_27612_12_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_28011_10_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_35418_7_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_23228_18_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_21402_31_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_22050_30_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_36847_10_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Severe ** GetHTSubSurfaceData: Surface W_36534_2_0_0_0_0 has an opaque surface construction; it should have a window construction.
** Warning ** CAUTION -- Interzone surfaces are occuring in the same zone(s).
** ~~~ ** ...use Diagnostics,DisplayExtraWarnings; to show more details on individual occurrences.
** Fatal ** Fatal error discovered in GetSurfaceData, see previous messages
...Summary of Errors that led to program termination:
..... Reference severe error count=18
..... Last severe error=GetHTSubSurfaceData: Surface W_36534_2_0_0_0_0 has an opaque surface construction; it should have a window construction.
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
*************
************* ===== Final Error Summary =====
************* The following error categories occurred. Consider correcting or noting.
************* Interzone surfaces - different zones
I don't really understand the message "** Severe ** GetHTSubSurfaceData: Surface W_35418_7_0_0_0_0 has an opaque surface construction; it should have a window construction."
What does it really mean for energy plus:?:
I first thought that the matter come from the material that i use, but i get the same error with the template already in DB library.
Can you help me, have you got any idea for me?
Thank you very much ,
Valentin
| Description: |
|
 Download |
| Filename: |
exaltis.dsb |
| Filesize: |
1.29 MB |
| Downloaded: |
236 Time(s) |
Last edited by vgrimaud on Mon Aug 04, 2008 12:58 pm; edited 1 time in total |
|
| Back to top |
|
 |
Andy Tindale

Posts: 1116 Location: Stroud |
Posted: Fri Jul 11, 2008 11:32 am Post subject: |
|
|
Hi Valentin,
The simulation fails because the number of layers on your glazing construction 'Projet de vitrage de toiture' has zero layers. I'm not sure why the zero layer option was in there but you should enter a value between 1 and 4. In future versions you will not be able to set zero layers.
Andy
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1116 Location: Stroud |
Posted: Fri Jul 11, 2008 11:43 am Post subject: |
|
|
By the way, it's a really nice model. Did you create it by drawing the profile of the building and extruding it horizontally, then cutting the building horizontally to create the stories?
Would you mind if we displayed a image of the model on our Visualisations webpage with some text to say that it was set up by you (a new user)?
Andy
|
|
| Back to top |
|
 |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 12:27 pm Post subject: |
|
|
Hi Andy!
Thanks a lot!
My simulation works fine now, but I get an other error. Energy+ said that I have non convex area so I need to run the simulation in full exterior mode. Well.. even if I am in Full exterior mode, I get the same message of error... It's strange, can you help me?
Thanks for the compliment! I drew the profile of each story, and extruded it horizontally. BTW, I would like to do something more complex on the building : I need to make a kind of hole in the north face of the building (like in the picture), but I have no idea how to proceed. Can you also help me here?
No problem if you display it on your visualization model, it's great!
Thank you in advance
| Description: |
|
| Filesize: |
61.27 KB |
| Viewed: |
501 Time(s) |

|
Last edited by vgrimaud on Fri Jul 11, 2008 1:06 pm; edited 1 time in total |
|
| Back to top |
|
 |
Andy Tindale

Posts: 1116 Location: Stroud |
Posted: Fri Jul 11, 2008 1:00 pm Post subject: |
|
|
Thanks for allowing us to use your model on our website!
First on including the 'hole'...
I think the only realistic way to include the 'hole' on the North face of the building would be to draw it in at the time of drawing the stories. You would have to start again with geometry to use this method.
Step 1. Draw the stories first but this time in plan view and extruding upwards using the dimensions of the largest storey. Use outline blocks without the sloping in the vertical but with the 'hole' on the North facade.
Step 2. Then draw a second similar large outline block to give the profile of the building alongside. This second building will be used to define the planes you will use to trim the storey outline blocks to give the vertical slopes.
Step 3. Then use these planes for cutting (read up documentation on cutting tool).
Step 4. Then convert the outline blocks to building blocks.
Andy
Last edited by Andy Tindale on Fri Jul 11, 2008 2:28 pm; edited 1 time in total |
|
| Back to top |
|
 |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 1:11 pm Post subject: |
|
|
Ok I get it!
I try right now and i show you the result!
Thanks!
|
|
| Back to top |
|
 |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 2:04 pm Post subject: |
|
|
Laurent_support figured out what was the matter with convex area : you need to be in full exterior for the simulation AND for the conception of air conditioning,if DB calculates automatically the dimension of the air conditioning system.
Best regards
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1116 Location: Stroud |
Posted: Fri Jul 11, 2008 2:27 pm Post subject: |
|
|
OK thanks for letting me know - I won't bother with the screenshots then!
Andy
|
|
| Back to top |
|
 |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 3:50 pm Post subject: |
|
|
Hi,
your solution works fine, but I think that the geometry of my building is too complex. The "hole" is not vertical, it's parallel to the curve of the curtain wall at the basis of the building, and get more vertical at each floor.. well, it's not very important, it's was just for the beauty of the building, not for the acuity of the simulation...
(but if you have a solution... )
Here is a little drawing of the profile of the building, with the "hole".
Regards,
Valentin
| Description: |
|
| Filesize: |
9.4 KB |
| Viewed: |
480 Time(s) |

|
|
|
| Back to top |
|
 |
Andy Tindale

Posts: 1116 Location: Stroud |
Posted: Fri Jul 11, 2008 4:05 pm Post subject: |
|
|
Looks like you didn't draw the 'holes' exactly lined up with the storey below when drawing the original stories? The original stories need to be all the same with the 'hole' looking like a slot going right up the building. Then use the profile of the outline building to cut the building to shape.
I've uploaded some images that may help you - they don't correspond exactly to your building but hopefully will convey the idea!
| Description: |
| Outline blocks showing the slot down the building and the profile block (the red one) used only to supply surfaces for cutting |
|
| Filesize: |
19.67 KB |
| Viewed: |
476 Time(s) |

|
| Description: |
| Outline blocks cut to the shape of the profile outline block (shown in red) |
|
| Filesize: |
20.49 KB |
| Viewed: |
476 Time(s) |

|
| Description: |
| Profile outline deleted and outlines converted to building blocks |
|
| Filesize: |
29.03 KB |
| Viewed: |
476 Time(s) |

|
|
|
| Back to top |
|
 |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 4:10 pm Post subject: |
|
|
In fact it seems that your solution is good, but just for convex surfaces, not for concave one, because when I use the cut tool, it cut too much building like you can see in the jpg.
| Description: |
|
| Filesize: |
10.6 KB |
| Viewed: |
474 Time(s) |

|
| Description: |
|
| Filesize: |
19.19 KB |
| Viewed: |
474 Time(s) |

|
|
|
| Back to top |
|
 |
vgrimaud
Posts: 8
|
Posted: Fri Jul 11, 2008 4:23 pm Post subject: |
|
|
| Andy Tindale wrote: | Looks like you didn't draw the 'holes' exactly lined up with the storey below when drawing the original stories? The original stories need to be all the same with the 'hole' looking like a slot going right up the building. Then use the profile of the outline building to cut the building to shape.
I've uploaded some images that may help you - they don't correspond exactly to your building but hopefully will convey the idea! |
Thanks for all your help, I think that I understand your idea, but the fact is that it's not possible if the "hole" isn't going right up the building. You cannot draw a hole that isn't absolutely vertical, can you?
Thanks again!
Valentin
|
|
| Back to top |
|
 |
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum You cannot attach files in this forum You can download files in this forum
|
Powered by p h p B B
|
|