International sales & support  DesignBuilder USA website  DesignBuilder Italy website  DesignBuilder Australia website  DesignBuilder France website  DesignBuilder Mexico website  DesignBuilder Portugal website
Home

Login

Username

Password

Remember me
Lost Password or Username?
No account yet? Register
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

how to generate or edit an epw file?

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> DesignBuilder Support
View previous topic :: View next topic  
Author Message
elena



Posts: 25
PostPosted: Fri Sep 01, 2006 8:33 pm    Post subject: how to generate or edit an epw file? Reply with quote

hi!
again another question..
i need to simulate the building like if i am using a stationary program (and not dinamic).
so the difference with the current way of working of design builder is the weather file (in the stationary program there's only one average temperature for all the month and in the dinamic one there's a different temperature for every hour)..
so i'd like to know how to generate or edit an .epw file in order to simulate the building in this other way.
thanks again.
this forum is very helpful...and patient! Wink
ele.
Back to top
View user's profile Send private message
Andy Tindale



Posts: 1111
Location: Stroud
PostPosted: Mon Sep 04, 2006 1:57 pm    Post subject: Reply with quote

Hi,

You can use DesignBuilder to carry out steady state EnergyPlus simulations directly by using the Heating design tab. In this case, the outside conditions are considered to be at the Winter design conditions as defined at the Site level and there is no solar radiation. Please note that when carrying out Heating design calculations, internal gains from occupants, lighting and other equipment are not used in the simulation.

Alternatively, as you say in your message, you could set up a steady state epw file. This can be done by exporting the epw file to csv format using the DesignBuilder weather data translator, editing the data as required in a spreadsheet program then converting back to epw format.

I just tested this procedure and it seems to work OK. I can't guarantee that you won't get (non-steady state) solar radiation on your external elements because EnergyPlus calculates the position of the Sun regardless of the data set in the epw file.

I'm glad to hear you find this forum useful Smile

Andy
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> DesignBuilder Support All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-6.