International sales & support DesignBuilder USA website DesignBuilder China website DesignBuilder Australia website DesignBuilder France website DesignBuilder Mexico website DesignBuilder Portugal website DesignBuilder Italy website DesignBuilder South Africa website DesignBuilder Brazil website DesignBuilder Japan website DesignBuilder Spain website DesignBuilder India website DesignBuilder Chile website
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Air Volume Flow Vector Output

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD
View previous topic :: View next topic  
Author Message
jean marais



Posts: 93
PostPosted: Wed Feb 03, 2010 9:43 am    Post subject: Air Volume Flow Vector Output Reply with quote

As we all know Q=VA, i.e. volume flow is equal to the area perpendicular velocity vector times that x-section area. Here we see the velocity vectors as out put.

It would be most helpful to help support AIRNET calculated natural ventilation rates, if one could somehow output the net air change rate in the zone, from the CFD calculation.
Back to top
View user's profile Send private message
Steve Potter



Posts: 562
Location: newcastle
PostPosted: Thu Feb 04, 2010 3:33 pm    Post subject: Reply with quote

Hi Jean,

In order to derive zone air change rates, all you need to do is to combine any specified supply diffuser air volumes and any opening air flow rates entering the zone (which you can obtain from the Tools->CFD Boundary Conditions dialog) with the zone volume included in the CFD calculation. i.e. ac/hr = (3600 x supply volume flow rate in m3/s) / zone volume in m3.

Regards,

Steve
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B