jean marais
Posts: 95
|
Posted: Wed Feb 03, 2010 9:43 am Post subject: Air Volume Flow Vector Output |
|
|
As we all know Q=VA, i.e. volume flow is equal to the area perpendicular velocity vector times that x-section area. Here we see the velocity vectors as out put.
It would be most helpful to help support AIRNET calculated natural ventilation rates, if one could somehow output the net air change rate in the zone, from the CFD calculation. |
|
| Back to top |
|
 |
Steve Potter

Posts: 572 Location: newcastle |
Posted: Thu Feb 04, 2010 3:33 pm Post subject: |
|
|
Hi Jean,
In order to derive zone air change rates, all you need to do is to combine any specified supply diffuser air volumes and any opening air flow rates entering the zone (which you can obtain from the Tools->CFD Boundary Conditions dialog) with the zone volume included in the CFD calculation. i.e. ac/hr = (3600 x supply volume flow rate in m3/s) / zone volume in m3.
Regards,
Steve |
|