International sales & support DesignBuilder USA website DesignBuilder China website DesignBuilder Australia website DesignBuilder France website DesignBuilder Mexico website DesignBuilder Portugal website DesignBuilder Italy website DesignBuilder South Africa website DesignBuilder Brazil website DesignBuilder Japan website DesignBuilder Spain website DesignBuilder India website DesignBuilder Chile website
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

CFD output velocity vector

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD
View previous topic :: View next topic  
Author Message
deepacha



Posts: 40
PostPosted: Tue Mar 09, 2010 8:29 am    Post subject: CFD output velocity vector Reply with quote

Hello,

I made a model with louvers using component blocks to do an external CFD analysis. (image attached)
I went ahead with the default CFD grid. The CFD simulations went upto 2500 iterations and did not converge.

I have a problem with the result. The louvers are inclined at 45degree pointing towards the ceiling. The incoming wind is 980fpm which is pretty high. I would expect the velocity vectors to go into the room upwards and then fall downwards in the middle or little further as they will have much lower velocities by then thereby going out through the outlet.

Instead the path of air flow seems completely the opposite. On closer look near the louvers, it looks like the velocity vectors are not affected by the louver geometry.

Could you please tell why this would happen or if I need to make changes in the model. I have also attached the image of the grid for your reference.



model grid.jpg
 Description:
 Filesize:  48.92 KB
 Viewed:  18152 Time(s)

model grid.jpg



45 plan.jpg
 Description:
 Filesize:  69.05 KB
 Viewed:  18152 Time(s)

45 plan.jpg


Back to top
View user's profile Send private message
deepacha



Posts: 40
PostPosted: Tue Mar 09, 2010 8:33 am    Post subject: Reply with quote

Hello,

Sorry, I had one more question that I forgot to include in my earlier post.

While setting up the CFD External Analysis, the wind speed was set as 980fpm. Then why would the velocity of the wind entering the model be around 437fpm ? This can be seen by the blue colored velocity vectors entering the model in the image attached with the previous post.

Thanks,
Deepa
Back to top
View user's profile Send private message
Steve Potter



Posts: 572
Location: newcastle
PostPosted: Wed Mar 10, 2010 8:58 am    Post subject: Reply with quote

Hi Deepa,

From your screenshots, it looks as if the grid spacing is too coarse to model the geometry of the louvres. You will need to ensure that the grid spacing is of a comparable dimension to the smallest dimension of the louvre.

As far as the wind velocity is concerned, the actual velocity varies from the ground level upwards according to the ASHRAE recommended wind profile.

Regards,

Steve



WindProfile.jpg
 Description:
ASHRAE wind profile
 Filesize:  27.12 KB
 Viewed:  18144 Time(s)

WindProfile.jpg


Back to top
View user's profile Send private message
deepacha



Posts: 40
PostPosted: Wed Mar 10, 2010 5:11 pm    Post subject: Reply with quote

Steve,

I tried refining the grid. Bu the aspect ratio increases a lot. I see that the grid has to be changed along the entire length or width of the model which increases the complexity and also refines the grid in unwanted spaces.

Is there a way to refine the grid only around the louver and not change across the length of the model ?

thanks,
Deepa
Back to top
View user's profile Send private message
Steve Potter



Posts: 572
Location: newcastle
PostPosted: Thu Mar 11, 2010 9:48 am    Post subject: Reply with quote

Deepa,

If you change the grid spacing for a region along one of the major axes, this spacing will be applied across the full extent of the remaining two axes. It is not currently possible to apply local refinements. If the number of grid cells is becoming excessive by reducing the grid spacing to accurately model the louvres, you may need to simplify the overall model.

Regards,

Steve
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> CFD All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B