International sales & support  DesignBuilder USA website  DesignBuilder Italy website  DesignBuilder Australia website  DesignBuilder France website  DesignBuilder Mexico website  DesignBuilder Portugal website  DesignBuilder South Africa website
Home

Login

Username

Password

Remember me
Lost Password or Username?
No account yet? Register
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Adjacent to ground bug

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation
View previous topic :: View next topic  
Author Message
taharvey



Posts: 57
PostPosted: Thu Feb 02, 2006 1:20 am    Post subject: Adjacent to ground bug Reply with quote

When I set the walls to "Adjacent to Ground", it disappears from the "heating design" graph of losses, from the HVAC requirement design calculation, and from the fabric losses in the simulation.

So a house with basements end up with unrealistic loss and HVAC calculations. How to fix?
Back to top
View user's profile Send private message
taharvey



Posts: 57
PostPosted: Fri Feb 03, 2006 4:35 am    Post subject: Reply with quote

Also, when a wall is set "Adjacent to Ground", the external wall construction type disappears from the construction tab. ?!?
Back to top
View user's profile Send private message
Andy Tindale



Posts: 1149
Location: Stroud
PostPosted: Fri Feb 03, 2006 7:51 am    Post subject: Reply with quote

Quote:
When I set the walls to "Adjacent to Ground", it disappears from the "heating design" graph of losses, from the HVAC requirement design calculation, and from the fabric losses in the simulation.

The default ground temperature is 16°C so the heat loss through surfaces adjacent to ground will be much lower than heat losses through surfaces adjacent to external air (and may appear be zero). The DesignBuilder default ground temperature is most appropriate for large buildings where the ground temperature 0.5 m below the building is typically 2°C lower than the average building internal temperature (EnergyPlus engineering reference document).

I think that this probably explains the results you're seeing. You may want to change these default ground temperatures defaults if you think the temperature of the ground on the other side of your surfaces adjacent to ground should be lower in your case.

We will be addressing the way ground temperatures are defined in future 1.x versions this year.

Quote:
Also, when a wall is set "Adjacent to Ground", the external wall construction type disappears from the construction tab. ?!?

This has now been fixed and ground adjacences work much more smoothly. The fix will be released in version 1.0.2 in the next few days and I will let you know when the new version is ready.

Regards
Andy
Back to top
View user's profile Send private message Visit poster's website
taharvey



Posts: 57
PostPosted: Fri Feb 03, 2006 8:39 am    Post subject: Reply with quote

Andy,

I did set the ground temperatures lower. In fact I set them to their minimum allowed value just to test the heating design tab. The graph bar disappears altogether, and isn't calcuated in the heating design calcs at all.
Back to top
View user's profile Send private message
Andy Tindale



Posts: 1149
Location: Stroud
PostPosted: Fri Feb 03, 2006 8:45 am    Post subject: Reply with quote

Please try version 1.0.2 when it is released - you should find that this problem has gone away.

Just to be double sure could you send in your model so I can check that it works with the new version?

Thanks
Andy
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-6.