Geert Bellens
Posts: 227
|
Posted: Sat Apr 14, 2012 9:54 am Post subject: Coldest setpoint manager doesn't seems to work ...? |
|
|
Using the "coldest" setpoint type I always get the following severe error :
** Warning ** The design coil load is zero for Coil:Heating:Water AIR LOOP ZONE AHU HEATING COIL
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Severe ** SetpointManager:Coldest="AIR LOOP/1/1/1/1/1 SETPOINT MANAGER", no zones with heating found:
** ~~~ ** Air Loop provides no heating, Air Loop="AIR LOOP ZONE".
Is this a bug in this setpoint? Or do I have to change some value in the heating coil parameters?
The message "no zones with heating found" is strange as the heating design gives me 20 kW heating...
Geert
Geert |
|
| Back to top |
|
 |
ecoeficiente.es
Posts: 53 Location: Spain |
Posted: Mon Apr 16, 2012 7:49 pm Post subject: |
|
|
That setpoint manager was intented only for dual duct systems and won't work with any other HVAC system type (according to E+ support).
The closest alternative is use SetpointManager:MultiZone:Heating:Average. Unfortunately it is not implemented in DB yet so you will have to change it directly in E+ idf file. |
|
| Back to top |
|
 |
Geert Bellens
Posts: 227
|
Posted: Mon Apr 16, 2012 8:29 pm Post subject: |
|
|
thanks
Geert |
|