Fail to run cooling design

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation
View previous topic :: View next topic  
Author Message
lordlms



Posts: 9
PostPosted: Tue Mar 20, 2007 3:28 pm    Post subject: Fail to run cooling design Reply with quote

Dear all

I dont know what happen to my design builder, i met this "Building 1 - Mechanical ventilation and natural ventilation in same zone not allowed with Simple HVAC data detail or for heating/cooling system sizing calculations." when i want to run the cooling design.

but i can run cooling deisgn when i change the natural ventilation off.

can anyone here help me..what should i setting should i change?

thanks a lot
Back to top
View user's profile Send private message
AOG



Posts: 85
PostPosted: Tue Mar 20, 2007 8:31 pm    Post subject: Reply with quote

lordlms,

If you want to simulate calcualted natural ventilation and mechanical ventilation simultaneously, you have to choose Compact HVAC in Model Option Data. Or, if you want to use simple HVAC, you have to choose scheduled ventilation in the same panel.

I hope it helps.

Best regards
Back to top
View user's profile Send private message Visit poster's website
bhandari



Posts: 89
PostPosted: Tue Mar 20, 2007 8:36 pm    Post subject: Reply with quote

AOG is right. I would also like to quote the following text from a previous discussion on this topic which may be of some help...

"it is possible to mix mechanical and natural ventilation provided you use Compact HVAC... but... Cooling Design calculations don't use Compact HVAC, they use the Simple 'purchased air' and EnergyPlus' simple Ventilation option. So when you carry out your Cooling design calculations, the combined mechanical and natural ventilation in the model cause problems.

The solution may be to switch off natural ventilation before carrying out the Cooling Design calculations to size cooling equipment. Then switch natural ventilation back on and carry out the simulation. You should use the 'Manual' or 'Autosize when not set' HVAC sizing option to avoid Cooling design calculations being carried out before every simulation. "

I hope it helps..

regards,

Mahabir
Back to top
View user's profile Send private message Visit poster's website
lordlms



Posts: 9
PostPosted: Wed Mar 21, 2007 6:56 am    Post subject: Reply with quote

Dear bhandari and AOG

I am a new user or DB here.
Thank you for helping me to solve this problem.

Best Regards
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-8.