International sales & support  DesignBuilder USA website  DesignBuilder Italy website  DesignBuilder Australia website  DesignBuilder France website  DesignBuilder Mexico website  DesignBuilder Portugal website  DesignBuilder South Africa website  DesignBuilder Brazil website
Home

Login

Username

Password

Remember me
Lost Password or Username?
No account yet? Register
  FAQFAQ    SearchSearch    Log in to check your private messagesLog in to check your private messages    UsergroupsUsergroups 

Natural ventilation and external openings operation

 
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation
View previous topic :: View next topic  
Author Message
Franck.Boutte



Posts: 13
PostPosted: Sat Jan 14, 2006 3:12 pm    Post subject: Natural ventilation and external openings operation Reply with quote

Hi,

I'm trying to model a natural ventilation , and I have some problems too.

I don't know the ach. I want to estimate the % of openings and the timing for in order to maintain a good temperature in summer (cooling design mode).

I check ventialtion as calculated in model options, in order to have ventilation calculated with wind pressures, buoyancy, and openings operation.

But, when I change the parameter for openings operation from 0% to 100% (with natural ventilation ach unchecked in HVAC tab), nor the external nor the external natural ventilation change.

I do not understand the results. What could be the problem ?

Thanks

Franck
Back to top
View user's profile Send private message
Andy Tindale



Posts: 1205
Location: Stroud
PostPosted: Sat Jan 14, 2006 5:37 pm    Post subject: Reply with quote

Hi Franck,

It's hard to be sure why you are getting no natural ventilation in your model but here is some information which hopefully will help to find out:

When the natural ventilation mode is 'Calculated', natural ventilation and infiltration heat loss/gain output data are displayed combined under 'External air' instead of 'External natural vent.' and 'Infiltration' data as it is on the Cooling design results screen.

One possible reason for getting zero 'External air' with calculated natural ventilation is that natural ventilation operation could be switched off on the operation schedule. This could be because the simulation period is in a holiday period and HVAC operation has been set to coincide with activity operation ('HVAC + natural ventilation operates with occupancy' building model option).

Also, if you are looking on the Cooling design tab and have Natural ventilation switched off on the HVAC tab then you will get no External natural vent. This is because calculated natural ventilation is not allowed in heating and cooling design simulations (scheduled natural ventilation data from the HVAC tab is used instead).

If this information doesn't help you to solve the problem, please post the model on the forum (see 'Add an Attachment' when you post a reply). Otherwise send it by e-mail to the support desk.

Best regards
Andy
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    DesignBuilder Forum Index -> EnergyPlus Simulation All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by p h p B B


DesignBuilder Software Ltd    +44  (0) 1453 755500      sales@designbuilder.co.uk      Terms and Conditions         

Copyright © DesignBuilder Software Ltd 2005-8.