Natural Ventilation

HVAC tab in model data

 

You can control the operation of natural ventilation using the data under the Natural Ventilation header on the HVAC tab. When using Calculated natural ventilation model option there is additional data on the Openings tab to control the timing and extent of operation of openings.

Note: the Natural ventilation checkbox must be ticked here on the HVAC tab to allow window, vent and door operation to be defined on the Openings tab.

The data shown under Natural ventilation on the HVAC tab depends on whether you are using the Scheduled or Calculated Natural ventilation setting in Model options.

Scheduled

When the Natural ventilation model option is set to Scheduled,and for heating and cooling design calculations, natural ventilation is defined simply as follows:

 

 

Find out more about Natural Ventilation Modelling under Modelling Issues.

Flow type

The Flow type defines the method used to set the maximum outside air natural ventilation rate. The options are:

 

 

m3/s = ac/h x ZoneVolume / 3600

 

where ZoneVolume is the actual air volume of the space calculated according to options for optionally excluding floor/ceiling constructions.

 

Note: this zone volume may be different from the value used for the purposes of calculating air flow rates for infiltration which uses the total zone volume.

 

                

m3s = MinFreshAir x NumberPeople / 1000

 

NumberPeople = Occupancy density (people / m2) * Zone floor area (m2)

MinFreshAir is the minimum fresh air rate per person (l/s/person)

      

 

Scheduled natural ventilation is active at any time in the simulation when:

 

 

 

Note: to avoid temperature control of natural ventilation set a very low Natural ventilation cooling setpoint temperature and to avoid temperature difference controlof natural ventilation set a high negative value of Max ventilation in-out delta T.

 

 

 

The actual natural ventilation rate at any one time in the simulation is calculated by multiplying the maximum natural ventilation rate (ac/h) by the value of the operation schedule.

 

When using the 'Typical workday' Timing option, natural ventilation can be either on or off. When it is on, the ventilation rate is the 'maximum natural ventilation rate'.

 

When using the 7/12 Timing option, it is possible to vary the natural ventilation rate between 0 and the maximum value by using daily profiles which have values between 0 and 100%.

Internal Windows, Doors and Vents

Airflow through external windows, vents, doors and holes are not modelled with Scheduled natural ventilation because the natural ventilation airflow from outside is explicitly defined (above). Internal windows, vents, doors and holes cause air to be exchanged between the two adjacent zones using the EnergyPlus 'Mixing' object. You can override operation of internal windows, vents, doors be off as follows:

 

Window, Vent, Door position

Override Off Action

Internal adjacent to unconditioned semi-exterior

Switch off the Natural ventilation 'On' checkbox in the occupied zone

Other internal

Unaffected by the Natural ventilation 'On' checkbox. Use the operation schedules on the Openings tab to switch off

Calculated

When the Natural ventilation model option is set to Calculated, natural ventilation is defined as follows:

 

 

You can override operation of windows, vents, doors to be off as follows:

 

Window, Vent, Door position

Override Off Action

External

Switch off the Natural ventilation 'On' checkbox

Internal adjacent to unconditioned semi-exterior

Switch off the Natural ventilation 'On' checkbox in the occupied zone

Other internal

Unaffected by the Natural ventilation 'On' checkbox. Use the operation schedules on the Openings tab to switch off

 

Note that even when operation is switched off as described above (or because operation schedules on the Openings tab are off) windows, vents and doors still provide a small flow path through the crack between the opening and the surrounding surface if the Model infiltration data is switched on.

 

 

Important Notes

 

  1. For cooling design calculations, natural ventilation is always handled as Scheduled even when the Natural ventilation model option is set to Calculated. In this case you can still enter natural ventilation air change rates and operation schedule data on the HVAC tab but it is used only for design simulations.

  2. With both the Scheduled and Calculated options, natural ventilation can be overrRelated Topicsidden to be off in Heating and Cooling design calculations. In Heating design calculations natural ventilation is switched off by default because it is considered to be a cooling mechanism - windows and vents will normally be closed during the coldest winter periods.

 

Mixed mode

You can also enter Mixed mode and data on opening Modulation under the Natural Ventilation header on the HVAC tab when using Calculated natural ventilation.

Control mode

For calculated natural ventilation you can define the control mode . The data can be entered at building, block or zone level. In the descriptions that follow:

 

Tout is the outdoor air temperature,

Tzone is the previous time step’s zone air temperature,

Tset is the Vent Temperature Schedule value,

Hzone is the specific enthalpy of zone air from the previous time step, and

Hout is the specific enthalpy of outdoor air.

 

The four allowed choices for natural ventilation Control mode are: