Data tab on Model Options dialog.
HVAC can be defined in DesignBuilder using:
This option controls how zone temperature and humidity setpoints as well as ventilation requirement and hot water consumption data is defined in Detailed HVAC. Two options are available:
The table below shows specifically where each item of Activity-related HVAC data is entered for the 2 options.
| 1-Simple HVAC | 2-Detailed HVAC | |
|---|---|---|
| Heating | ||
| Heating setpoint temperature |
Heating setpoint temperature (Activity Tab) |
HVAC Zone, Heated floor, Chilled ceiling dialogs |
| Heating setback temperature |
Heating setback temperature (Activity Tab) |
HVAC Zone, Heated floor, Chilled ceiling dialogs |
| Heating operation schedule |
Heating operation schedule (HVAC Tab) |
HVAC Zone dialog, Heated floor, Chilled ceiling dialogs |
| Cooling | ||
| Cooling setpoint temperature |
Cooling setpoint temperature (Activity Tab) |
HVAC Zone, Heated floor, Chilled ceiling dialogs |
| Cooling setback temperature |
Cooling setback temperature (Activity Tab) |
HVAC Zone, Heated floor, Chilled ceiling dialogs |
| Cooling operation schedule |
Cooling operation schedule (HVAC Tab) |
HVAC Zone dialog, Heated floor, Chilled ceiling dialogs |
| Humidity Control | ||
| Humidification setpoint |
Humidification setpoint (Activity Tab) |
HVAC Zone dialog |
|
Dehumidification setpoint |
Dehumidification setpoint (Activity Tab) |
HVAC Zone dialog |
| Ventilation | ||
|
Minimum fresh air per person |
Minimum fresh air per person (Activity Tab) |
HVAC Zone dialog |
|
Minimum fresh air per floor area |
Minimum fresh air per floor area (Activity Tab) |
HVAC Zone dialog |
| DHW | ||
| DHW consumption rate |
DHW consumption rate per floor area (Activity Tab) |
HVAC Zone dialog |
| DHW operation schedule |
DHW operation schedule (HVAC Tab) |
Water outlet dialog |
| Temperature Control | ||
|
Heated floors and Chilled ceilings |
Temperature Control (Simulation Calculation Options Dialog) |
Heated floor, Chilled ceiling dialogs |
Note: For heating and cooling design calculations the humidity and temperature setpoints and ventilation requirement data comes from the Activity and HVAC tabs as described under the 1-Simple HVAC column in the above table, regardless of the Detailed HVAC Activity Data setting.
When using Simple HVAC, you can choose whether to specify some basic details on the system. If you activate this option then you will be able to specify:
Mechanical ventilation method
If you switch this option off then any heating or cooling is assumed to be entirely convective.
This option might be switched off for early design stage architectural use to simplify the HVAC data entry.
When using Simple HVAC and you choose to specify Simple HVAC details (above), there are 3 options for modelling fans, pumps and other auxiliary energy associated with the HVAC system:
This option defines how mechanical ventilation is treated for Simple HVAC Simulation and Cooling design calculations. Options are:
When using Simple and Compact HVAC, DesignBuilder can automatically calculate heating and cooling capacity in each zone based on the output from the Heating and Cooling design calculations. The Plant sizing model option provides control over how heating and cooling capacities are set for Simulations. Select from:
These HVAC sizing options are described below.
Note: In Heating and Cooling design calculations, heating and cooling loads are always met and so this option does not apply - it only applies to Simulations.
The effect of this option depends on the HVAC model option. When using Simple HVAC, equipment is modelled as having unlimited capacity allowing it to meet any heating or cooling demand and setpoint temperatures are always maintained. This option can cause extremely large peaks in heating and cooling delivery to zones and will tend to over-predict heating and cooling energy and under predict discomfort hours. When using Compact HVAC this option is equivalent to 3-Autosize and the Compact HVAC autosizing mechanism is used to size the components and flow rates to ensure that the required comfort conditions are met.
No heating and cooling sizing calculations are required in this case.
Heating and cooling capacity Model data must be entered manually. Choose this option if you have specific heating and cooling capacity data you wish to use and do not want it to be overwritten when model data or model options change.
If you would like DesignBuilder to calculate the heating and cooling sizes and also maximum supply flow if you are using Compact HVAC you should follow this procedure:
If you are using the Manual sizing option together with Compact HVAC and wish to use different cooling sizes to those obtained from looking at the output of previous EnergyPlus autosizing calculations (e.g . from eplusout.eio) you will need to ensure that the maximum supply flow is changed accordingly. If you increase the maximum cooling capacity but don't increase the Maximum supply flow rate (or even leave it as Auto) you will get "Rated air volume flow rate per watt of rated total cooling capacity is out of range" errors in the EnergyPlus simulation because the cooling capacity requested cannot be achieved with the specified air flow rate. Also due to a quirk in EnergyPlus, the Auto Maximum supply flow rate option does not work well with Manual sizing option and automatically calculated Maximum supply flow rates do not account for the 'higher than autosized' cooling capacity requested.
Autosize is the default option where heating and cooling capacities are always calculated prior to each simulation and the heating and cooling capacity model data is not displayed. When using Simple HVAC the heating and cooling design calculations will be run as required before the simulation to calculate the required sizes. When using Compact HVAC the components and flow rates are sized using the EnergyPlus autosizing mechanism to ensure that the required comfort conditions are met. In this case heating and cooling autosizing calculations are done internally within EnergyPlus and no extra autosizing calculations are carried out by DesignBuilder.
In this case heating and cooling capacities are autosized and loaded into model data following heating and cooling design simulations. If Capacity model data is not present before a simulation, it is generated by automatically by carrying out heating and cooling design calculations and is written into the HVAC model data.
You should be aware that when using the 4-Autosize when not set option, the heating/cooling zone capacity model data is not treated the same way as other calculated results. In general, calculated results are deleted when any edit is made to the building model, but this is not the case for zone capacity model data. This is only updated when:
If you always want the heating capacity to be kept up-to-date with your model and do not have any specific capacity sizes you wish to use, you should consider using the 3-Autosize option. This will cause autosizing to be carried out prior to every simulation.
You can change heating capacities by hand if you wish but you should bear in mind that, if Model options change, all heating and cooling capacities are reset to zero. Set the option to 2-Manual to avoid this happening.