Openings tab in model data under External Glazing, Internal Glazing and Roof Glazing headers
The operation of windows can be defined by entering data under Operation headers. The data will depend on the Natural ventilation model option set:
The % Glazing area opens slider allows you to define the openable window area as a percentage of the total window area. For example enter '20' if 20% of the window area can open.
Note: if modulation is switched on (it is by default) the glazing opening areas are multiplied by a factor to account for external conditions.
You can also enter a schedule to define the timing of the window operation.
The windows are 'open' when:
Tzone_air > Tsetpoint AND Tzone_air > Toutside_air AND the schedule value = 1
The ventilation rate is calculated based on the pressure difference across the opening calculated from wind and stack pressure effects using equations described in Natural Ventilation Modelling.
Airflow through external windows, vents, doors and holes are not modelled with Scheduled natural ventilation because the natural ventilation airflow from outside is explicitly defined using the total natural ventilation flow rate and operation on the HVAC tab. No operation data is entered on the Openings tab for external windows in this case.
Note: Natural Ventilation can be overridden to be off on the HVAC tab for both Calculated and Scheduled model options.