HVAC tab in model data under Mechanical Ventilation header
With Compact HVAC, you can specify air-to-air heat recovery which is available between the relief air stream and the outside air inlet stream. Heat recovery is selected for Unitary multizone, CAV and VAV systems by checking Heat Recovery On under the Mechanical Ventilation header at building level. For Unitary single zone make the selection at the zone level.
Enter the type of air-to-air heat recovery. The choices are:
1-Sensible - recovers sensible heat
2-Enthalpy - recovers sensible and latent heat.
Enter the sensible heat recovery effectiveness. This is applied as a constant effectiveness at all conditions. The valid range is from 0.0 to 1.0, and the default is 0.70.
Enter the latent heat recovery effectiveness if Heat Recovery Type is Enthalpy. This is applied as a constant effectiveness at all conditions. The valid range is from 0.0 to 1.0, and the default is 0.65.
When no economiser is selected this data defines the heating setpoint temperature of the heat recovery device for Unitary and Unitary multizone systems. Note that the single value is applied throughout the year. For example enter 15C to model a system which heats outside air up to 15C and no higher. A high setpoint value will provide optimal heating but this may add to cooling loads in the summer.
If an economiser option is selected, the heat recovery is bypassed whenever the economiser operates and the heat recovery is always bypassed if economiser operation would be beneficial.
The heat recovery will operate when:
Heat recovery is switched on at the building level for VAV and unitary multizone systems and at zone level for Unitary single zone and Fan coil systems AND
When economiser operation is off.
You can have heat recovery and no Economiser action by switching on Heat recovery and setting economiser to 1-None. In this case the heat recovery units heats outside air using the Heat recovery heating setpoint temperature above. It also cools outside air when return air temperature is lower than outside air temperature.
When heat recovery is used with the 2-Full fresh air outside air mixing option in CAV/VAV systems, the heat recovery is by-passed when this is advantageous in reducing AHU heating/cooling coil loads. Otherwise, when using the 1-Recirculation option, the economiser must be selected in the interface for the heat recovery to be by-passed in this way.