Model Geometry Example

This section documents the way the DesignBuilder model geometry you define is used in the calculations and visualisations. The description is based on the Model Geometry Example.dsb example building shown below. The file Model Geometry Example.dsb is supplied with DesignBuilder. The model consists of 4 blocks, each block containing a single zone, except the Ground floor block which is divided into equal sized North and South zones.

 

 

 

and Visualisation view:

 

 

See the Visualisation Limitations section for information on some minor differences in the rendered images and the model used in the calculations.

 

The model consists of:

 

1 x 10m x 10m Ground floor block partitioned into equal size North and South zones using partition of thickness 0.05m.

1 x 10m x 10m First floor block stacked on ground block.

1 x 10m x 5m Block with flat roof and external floor connects with the First floor block on the North side.

1 x 10m x 10m Roof block with 45° roof slope drawn in the vertical plane and extruded horizontally, i.e. it is not defined as a Pitched roof block form. The Roof block is stacked on top of the First floor block.

 

Above are external block dimensions.

Block wall thickness = 0.2m for all blocks.

30% Glazing ratio for all blocks, all glazing uses default facades (i.e. no windows or doors have been drawn).

Model uses default Zone volume calculation options - Internal floor constructions not subtracted from zone volume, External floor constructions not subtracted from zone volume  and Ground floor construction is below ground and is not subtracted from zone volume.

 

When exported to 3-D DXF using the Whole model with details option and dimensioned the model looks like this:

 

 

The same model in 3-D view looks like this:

 

 

The ceiling / floor surface between First floor block - Zone 1 and Roof block - Zone 1 has area 9.6m x (9.6 - 2 x 0.2 / sin 45°)  where the 0.2 / sin 45° term is the Roof block wall thickness (0.2m) adjusted to account for the roof slope (45°) as shown in the diagram below.

 

The dimension data for the zones, surfaces and openings used in the calculations can be seen in the Navigator and can also be obtained by exporting a csv report file.

 

The general principles used in DesignBuilder are:

 

 

The tables below list the most important geometric data and show how each item is calculated. Note that surfaces with glazing have area of glazing subtracted. The areas below are consistent with EnergyPlus and SBEM calculations. Klima Europa calculations have modifications to wall area and volume calculations to ensure internal heights are used.

 

Zone Ground floor block - North

 

Calculation Note

Floor area (m2)

46.08

4.8m x 9.6m

Volume (m3)

138.24

46.08m2 x 3m (subtract volume of ground floor if Ground floor construction is below ground and is not subtracted from zone zolume model option set)

 

Surface

Area (m2)

Area Calculation Note

Adjacency (Orientation / adjacent zone)

Ground floor

46.08

4.8m x 9.6m

Ground

Ceiling

46.08

4.8m x 9.6m

First floor block - Zone 1

Wall Outside

10.08

4.8m x 3m - glazing area on surface (2.88m x 1.5m)

90

Glazing Outside

4.32

2.88m x 1.5m

90

Wall Outside

20.16

9.6m x 3m - glazing area on surface (5.76m x 1.5m)

0

Glazing Outside

8.64

5.76m x 1.5m

0

Wall Outside

10.08

4.8m x 3m - glazing area on surface (2.88m x 1.5m)

270

Glazing Outside

4.32

2.88m x 1.5m

270

Partition

28.8

9.6m x 3m

Ground floor block - South

 

 

Zone Ground floor block - South

 

Calculation Note

Floor area (m2)

46.08

4.8m x 9.6m

Volume (m3)

138.24

46.08m2 x 3m (subtract volume of ground floor if Ground floor construction is below ground and is not subtracted from zone volume model option set)

 

Surface

Area (m2)

Area Calculation Note

Adjacency (Orientation / adjacent zone)

Ground floor

46.08

4.8m x 9.6m

Ground

Ceiling

46.08

4.8m x 9.6m

First floor block - Zone 1

Wall Outside

10.08

4.8m x 3m - glazing area on surface (2.88m x 1.5m)

90

Glazing Outside

4.32

2.88m x 1.5m

90

Wall Outside

20.16

9.6m x 3m - glazing area on surface (5.76m x 1.5m)

180

Glazing Outside

8.64

5.76m x 1.5m

180

Wall Outside

10.08

4.8m x 3m - glazing area on surface (2.88m x 1.5m)

270

Glazing Outside

4.32

2.88m x 1.5m

270

Partition

28.8

9.6m x 3m

Ground floor block - North

 

 

First floor block - Zone 1

 

Calculation Note

Floor area (m2)

92.16

9.6m x 9.6m

Volume (m3)

276.48

92.16m2 x 3m (subtract volume of ground floor if Ground floor construction is below ground and is not subtracted from zone volume model option set)

 

Surface

Area (m2)

Area Calculation Note

Adjacency (Orientation / adjacent zone)

Floor

46.08

4.8m x 9.6m

Ground floor block - North

Floor

46.08

4.8m x 9.6m

Ground floor block - South

Ceiling

90.569

9.434m x 9.6m (9.434m = 10 - 2 x 0.2 / sin 45°)

Roof block - Zone 1

Wall Outside

20.16

9.6m x 3m - glazing area on surface (5.76m x 1.5m)

90

Glazing Outside

8.64

5.76m x 1.5m

90

Wall Outside

20.16

9.6m x 3m - glazing area on surface (5.76m x 1.5m)

180

Glazing Outside

8.64

5.76m x 1.5m

180

Wall Outside

10.08

9.6m x 3m - glazing area on surface (5.76m x 1.5m)

270

Glazing Outside

8.64

5.76m x 1.5m

270

Wall (with hole)

0.201

Necessary surround for interblock partition

0

Interblock partition

28.649

Interblock partition 9.6m x 3m - wall (with hole) (0.201m2)

Block with flat roof and external floor - Zone 1

 

 

Block with flat roof and external floor - Zone 1

 

Calculation Note

Floor area (m2)

44.16

4.6m x 9.6m

Volume (m3)

132.48

44.16m2 x 3m (subtract volume of external floor if Internal and external floor construction is below ground and is not subtracted from zone volume model option set)

 

Surface

Area (m2)

Area Calculation Note

Adjacency (Orientation / adjacent zone)

Floor

44.16

4.6m x 9.6m

Outside

Flat roof

44.16

4.6m x 9.6m

Outside

Wall Outside

9.66

4.6m x 3m - glazing area on surface (2.76m x 1.5m)

90

Glazing Outside

4.14

2.76m x 1.5m

90

Wall Outside

20.16

9.6m x 3m - glazing area on surface (5.76m x 1.5m)

0

Glazing Outside

8.64

5.76m x 1.5m

0

Wall Outside

9.66

4.6m x 3m - glazing area on surface (2.76m x 1.5m)

270

Glazing Outside

4.14

2.76m x 1.5m

270

Wall (with hole)

0.201

Necessary surround for interblock partition

180

Interblock partition

28.649

Interblock partition 9.6m x 3m - wall (with hole) (0.201m2)

First floor block - Zone 1

 

 

Roof block - Zone 1

 

Calculation Note

Floor area (m2)

90.569

9.434m x 9.6m (9.434m = 10 - 2 x 0.2 / sin 45°)

Volume (m3)

213.615

90.569m2 x (5m - 0.2 / cos 45°)  x 0.5

 

Surface

Area (m2)

Area Calculation Note

Adjacency (Orientation / adjacent zone)

Floor

90.569

9.434m x 9.6m (9.434m = 10 - 2 x 0.2 / sin 45°)

First floor block - Zone 1

Wall Outside

15.576

9.434m x (5m - 0.2 / cos 45°)  x 0.5 - glazing area (6.676)

90

Glazing Outside

6.676

4.45m x 1.5m

90

Wall Outside

15.576

9.434m x (5m - 0.2 / cos 45°)  x 0.5 - glazing area (6.676)

270

Glazing Outside

6.676

4.45m x 1.5m

270

Roof (slope 45° )

64.042

6.671m x 9.6m, 6.671 is the internal eaves to apex length = (5 - 0.2 / cos 45) / sin 45

90

Roof (slope 45° )

64.042

6.671m x 9.6m, 6.671 is the internal eaves to apex length = (5 - 0.2 / cos 45) / sin 45

270

 

Additional information for Klima Europa users

The DesignBuilder interface to Klima Europa works slightly differently. With Klima Europa, calculations have modifications to wall area and volume calculations to ensure internal heights are used. A ratio is used to do this:

 

InnerVolumeToOuterVolumeRatio = (Volume - ConstructionVolumeForSubtraction) / Volume

 

The area of all vertical walls is multiplied by the above factor to ensure that only internal wall areas are used in calculations. Also the volume is reduced to account for internal and external floor constructions (but not by default for ground floors as these are by default taken as being below ground).

 

To achieve this Klima users should make the Zone volume calculation settings before running Klima Europa:

 

Zone volume calculation option

Recommended Setting for Klima Europa

Internal floor constructions not subtracted from zone volume

No

External floor constructions not subtracted from zone volume

Yes

Ground floor construction is below ground and is not subtracted from zone volume

Yes

 

These settings may be enforced when in Klima analysis mode in future versions.

Other related information

  1. Block and Zone Dimensions is an introductory section explaining how to enter blocks and the relationship with zones.
  2. Also see Constructions for how to edit the construction configuration.

  3. See Combined Constructions for information on the meaning of the Construction Model data.