HVAC tab in model data
You can control the operation of natural ventilation using the data under the Natural Ventilation header on the HVAC tab. When using Calculated natural ventilation model option there is additional data on the Openings tab to control the timing and extent of operation of openings.
When the Natural ventilation model option is set to Scheduled, natural ventilation is defined simply as follows:
Check the 'On' checkbox under the Natural Ventilation header.
Select the flow type
Set the maximum zone natural ventilation rate in air changes per hour (if flow type is 1-By zone).
Enter the operation information.
Find out more about Natural Ventilation Modelling under Modelling Issues.
Defines the method used to set the maximum outside air natural ventilation rate. The options are:
1-By zone - enter the zone natural ventilation rate in air changes per hour in the control directly below. The air flow rate is calculated from the ac/h data using:
m3/s = ac/h x ZoneVolume / 3600
where ZoneVolume is the actual air volume of the space calculated according to options for optionally excluding floor/ceiling constructions.
Note: this zone volume may be different from the value used for the purposes of calculating air flow rates for infiltration which uses the total zone volume.
2-Min fresh air per person - maximum natural ventilation rate is defined using Minimum fresh air requirements as set on the Activity tab. The air flow rate in m3/s is calculated as:
m3s = MinFreshAir x NumberPeople / 1000
NumberPeople = Occupancy density (people / m2) * Zone floor area (m2)
MinFreshAir is the minimum fresh air rate per person (l/s/person)

Scheduled natural ventilation is active at any time in the simulation when:
The air temperature in the zone is higher than the Ventilation cooling set-point temperature (as set on the Activity tab under the 'Environmental Comfort' header) AND ...
The difference between inside and outside air temperatures (Tin - Tout) is less than 'Max ventilation in-out delta T' (below the Ventilation cooling setpoint data on the Activity tab) AND ...
The operation schedule is on at that time in the simulation.
Note: to avoid temperature control of natural ventilation set a very low Ventilation cooling setpoint temperature and to avoid temperature difference control of natural ventilation set a high negative value of Max ventilation in-out delta T.
The actual natural ventilation rate at any one time in the simulation is calculated by multiplying the maximum natural ventilation rate (ac/h) by the value of the operation schedule.
When using the 'Typical workday' Timing option, natural ventilation can be either on or off. When it is on, the ventilation rate is the 'maximum natural ventilation rate'.
When using the 7/12 Timing option, it is possible to vary the natural ventilation rate between 0 and the maximum value by using daily profiles which have values between 0 and 100%.
Airflow through external windows, vents, doors and holes are not modelled with Scheduled natural ventilation because the natural ventilation airflow from outside is explicitly defined (above). Internal windows, vents, doors and holes cause air to be exchanged between the two adjacent zones using the EnergyPlus 'Mixing' object. You can override operation of internal windows, vents, doors be off as follows:
|
Window, Vent, Door position |
Override Off Action |
|
Internal adjacent to unconditioned semi-exterior |
Switch off the Natural ventilation 'On' checkbox in the occupied zone |
|
Other internal |
Unaffected by the Natural ventilation 'On' checkbox. Use the operation schedules on the Openings tab to switch off |
When the Natural ventilation model option is set to Calculated, natural ventilation is defined as follows:
Check the 'On' checkbox under the Natural Ventilation header.
On the Openings tab by setting window, door and vent opening sizes and operation times.
You can override operation of windows, vents, doors be off as follows:
|
Window, Vent, Door position |
Override Off Action |
|
External |
Switch off the Natural ventilation 'On' checkbox |
|
Internal adjacent to unconditioned semi-exterior |
Switch off the Natural ventilation 'On' checkbox in the occupied zone |
|
Other internal |
Unaffected by the Natural ventilation 'On' checkbox. Use the operation schedules on the Openings tab to switch off |
Note that even when operation is switched off as described above (or because operation schedules on the Openings tab are off) windows, vents and doors still provide a small flow path through the crack between the opening and the surrounding surface if the Model infiltration data is switched on.
Note 1: for Cooling design simulations, natural ventilation is always handled as Scheduled even when the Natural ventilation model option is set to Calculated. In this case you can still enter natural ventilation data on the HVAC tab and it is used only for design simulations.
Note 2: Natural ventilation is not included in Heating design calculations as it is considered to be a cooling mechanism - windows and vents will be closed during the coldest winter periods.