Surface Convection

Construction tab in model data under Construction header

 

You can select the inside and outside surface convection algorithms in the Model data on the Construction tab under the Surface Convection header.  This provides you with the option of making different selections in different parts of the building.

Inside convection algorithm

You can select from a range of EnergyPlus inside convection algorithms for calculating the convection between internal zone surfaces and the rest of the zone air in the simulation calculations:

 

 

To avoid discontinuities in surface heat transfer rate calculations, all correlations are extrapolated beyond the lower limit of the data set (3 ACH) to a natural convection limit which is applied during the hours when the system is off. These models are explained in greater detail in the EnergyPlus Engineering Reference Document.

Outside convection algorithm

You can select from a range of EnergyPlus outside convection algorithms:

 

 

These are convection-only heat transfer coefficients; radiation heat transfer coefficients are calculated automatically by the program. All algorithms are described more fully in the EnergyPlus Engineering Reference.

 

When the surface is wet (i.e. it is raining and the surface is exposed to wind) then the convection coefficient appears in results as a very large number (1000) and the surface is exposed to the Outdoor Wet Bulb Temperature rather than the Outdoor Dry Bulb Temperature.

 

Inside and Outside convection algorithm settings can be made in various places.

 

 

You cannot make changes to individual surface convection settings where the surface is an internal partition.

 

Note: the equivalent inside and outside surface convection options in the Calculation and Model options dialogs control building default values (equivalent of making a setting in Model data at building level) and changes at block, zone or surface levels in the Model data will override these settings.